#58177 - 11/01/05 07:10 PM Smallest 3 phase panel  
maintenanceguy  Offline
Member
Joined: Dec 2001
Posts: 300
Southern NJ, USA
We're building alot of small computer server rooms in all fo the schools in our district.

Each of these is nearly identical and needs a specific number of 120 and 208V recepticles. We've only done a couple so far and pulled each circuit from nearby panels but some weren't all that nearby.

With more than a dozen to go, I got the brilliant idea of installing a small subpanel in each server room. this means pulling less wire and gives easy room to expand in the future.

I need a small three phase electrical panel. The ideal panel would be 60A with 6 breaker positions but something a little larger would work. I'm not so concerned about size (although in some of these closets it is a problem). I'm mostly concerned with capacity. I don't have an available 200A near some of these locations.

The smallest panel I've seen is a 100A 24 position - Much more than I need.

Anybody know of a smaller one?


Work Gear for Electricians and the Trades

#58178 - 11/01/05 07:56 PM Re: Smallest 3 phase panel  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
How about buying the 100A and replacing the main with a 60A that you buy separately?


Ron

#58179 - 11/01/05 08:58 PM Re: Smallest 3 phase panel  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,857
Brick, NJ USA
M-GUY:
Square d
QO403L60NS; 3 CIRC, 60 AMP, MLO
QO312L125G; 12 CIRC, 125 AMP, MLO

Both are main lug only panels.

John


John

#58180 - 11/02/05 01:03 AM Re: Smallest 3 phase panel  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Why does he need a main. Use the 100 main lug panel and supply it with whatever size overcurrent device ahead of it, as long as the device is not more than 100 amps.


Pierre Belarge


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.002s) Memory: 0.7604 MB (Peak: 0.8916 MB) Zlib enabled. Server Time: 2017-08-16 17:14:02 UTC