... We're doing a 300 amp. underground service for a residence,and I know that I need to insert an expansion coupling,..but where?? on the line side schedule 80 pvc,just before the meter,or in the trench,...and do I also need one on the load side before entering the basement through the foundation??

I realize it depends on the length of run and the expected change in ambient temperature, but I'm a little fuzzy on where to place it...(don't be funny, I know what you're about to say..)
Russ


.."if it ain't fixed,don't break it...call a Licensed Electrician"
Work Gear for Electricians and the Trades
Re: Expansion coupling... #57728
10/19/05 12:07 AM
10/19/05 12:07 AM
T
Tesla  Offline
Member
Joined: Jun 2004
Posts: 1,273
Sacramento, CA
Fully buried PVC is not prone to expansion issues.

The expansion joint would be needed if the length of exposed run is more than stubbing out to a panel/ meter pan.

Buried runs usually do not have expansion joints since the ground greatly moderates their temperature swings.


Tesla
Re: Expansion coupling... #57729
10/19/05 07:38 AM
10/19/05 07:38 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
Hear-say (from the photo discussion area on ECN [Linked Image], rather than personal experience: for a short stub of pvc from underground to the meter pan, the thermal expansion will not be enough to matter. Thermal expansion and contraction shows up as a percentage change in length, so the shorter the 'nominal' length, the smaller the change produced by thermal effects.

However the expansion joint will also nicely accommodate things like the soil settling after construction, or the earth moving for other reasons. If you search in the Photos Submitted for Discussion area, I'm sure you will find pictures of residential service stubs ripped out of meter pans by the ground settling.

-Jon

Re: Expansion coupling... #57730
10/19/05 09:53 PM
10/19/05 09:53 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
As Jon stated, ground movement is a problem that can be solved by using an expansion fitting and is one method of compliance with 300.5(J).
Don


Don(resqcapt19)
Re: Expansion coupling... #57731
10/20/05 07:39 PM
10/20/05 07:39 PM
HotLine1  Offline

Member
Joined: Apr 2002
Posts: 7,069
Brick, NJ USA
Rat:

IF you run pvc from meter pan (at house) to pole, & up the obligatory 10'; you need an expansion joint between the ma at the meter pan, and the dirt.

IF you only have to 'leave' a short pvc piece, with the bell/bushing; for BUD direct burial by utility; you do NOT need an exp. joint.

As Jon & Don said....ground heaving, not expansion in this case.

(From another Jersey Guy)

John


John

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 9
Popular Topics(Views)
253,292 Are you busy
189,905 Re: Forum
179,625 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.025s Queries: 14 (0.005s) Memory: 0.9685 MB (Peak: 1.1077 MB) Zlib enabled. Server Time: 2019-02-22 02:42:19 UTC