Joined: Mar 2005
Posts: 49
R
Member
The service will be 208V, 3-phase, 4-wire.
Main service disconnect will be 100 Amp

The service entrance equipment will be located in an outdoor, weatherproof and heated enclosure. The enclosure also encloses a control system for a concrete sewage lift station with a bottom at 18 feet below grade.

One of the main considerations is that the ground freezes during the winter. I've also heard that the permafront is 1800 feet deep in places around Skagway.

Do you have any thoughts the design of a good grounding electrode system be that provides the necessary grounding (earthing) protection year round??

Thanks for your comments, your expert help is much appreciated.
Rich Thomas

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Oct 2004
Posts: 265
D
Member
I'm not sure how freezing would be a problem for the GES? Though I live and work in sunny SoCal [Linked Image]

Joined: Sep 2005
Posts: 106
J
Member
eight foot ground rods?


Mike
Joined: Jul 2005
Posts: 46
R
Member
Using a concrete encased electrode would be a good bet. [Linked Image]

The requirement for footings to be below frost depth would help out with your concerns.

Chris

Joined: Jan 2003
Posts: 1,429
L
LK Offline
Member
Stop in the chat room one evening after 10pm EST we have a few electricians from that area.

Joined: Jul 2004
Posts: 10,048
Likes: 38
G
Member
It may be too late for this one but a Ufer in the bottom of that collection tank is probably as good as it gets.


Greg Fretwell
Joined: Mar 2005
Posts: 49
R
Member
Thanks to all those who responded.

Since posting my question I've found that the ground in Skagway doesn't freeze very deeply, so an industry standard type grounding electrode system is adequate.

However, gfretwell's idea using the wet well rebar as a ufer will be part of the system.

Thanks again,
Rich

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Sep 2003
Posts: 650
W
Member
Just to bump dmattox's question, because I'd like to know more.

Quote

I'm not sure how freezing would be a problem for the GES?

My understanding is that the conductivity of soil/clay/earth depends upon the ionic conduction, where ionized atoms physically _move_, rather than metallic conductivity. If the ground freezes, then the conductivity can drop in much the same way as a GES in soil that becomes very dry. At least that is my weak understanding. I'd love to learn more on this topic.

-Jon

Joined: Jul 2005
Posts: 57
D
Member
How about Conducrete??
http://www.saeinc.com/Conducrete

Joined: Mar 2005
Posts: 49
R
Member
I'll give Conducrete a looksee. Thanks distributor x.

Rich