#57154 10/05/05 11:50 PM
Joined: Aug 2005
Posts: 89
D
Member
Well the same thing with the grounding conductor, even if it's 4 grounds in there, it's still 1. I guess the clamps will apply the same concept.

#57155 10/06/05 01:42 PM
Joined: Feb 2002
Posts: 840
C
Member
I believe the answer is 10 #12 conductors.


Peter


Peter
#57156 10/06/05 03:30 PM
Joined: Jul 2005
Posts: 46
R
Member
314.16 (B) (4): For each yoke or strap containing one or more devices or equipment, a double volume allowance in accordance with table 314.16 (B) shall be made for each yoke or strap based an the largest conductor connected to a device(s) or equipment supported by that yoke or strap.

Simply stated you count 2 wires for each yoke. [Linked Image]

Chris

#57157 10/06/05 05:15 PM
Joined: Sep 2005
Posts: 421
Member
since the grounding conductor on the device originates outside the box it is counted a .....1, this counts as an additional EGC...250.146 and 316.16(B)(5) any jumpers that stay in the box are not counted

total is therefore ....11


Tom
#57158 10/06/05 06:32 PM
Joined: Mar 2001
Posts: 2,056
R
Member
togol,

Good observation, but I think you are referring to an additional IG grounding conductor.

I count...10

[This message has been edited by Redsy (edited 10-06-2005).]

#57159 10/06/05 07:31 PM
Joined: Sep 2005
Posts: 421
Member
Redsy.
....yep there it is,

I also typed the wrong reference ....should be ....314.16 (B)(5)
but it does seem to contradict ......(1) of the same section !


Tom