transfomer taps #55779
09/06/05 04:14 PM
09/06/05 04:14 PM
J
jtorres  Offline OP
Junior Member
Joined: Sep 2005
Posts: 6
San Antonio, Texas
Hello everybody
I`m new to this site and what I`ve seen so far I think this is a great forum.

I was having a discussion with another student of the trade and we couldn`t agree on the following statement.
" Taps are usually provided on the secondary low-voltage side at 2 1/2 percent incraments to correct the phase angle of the secondary voltage"
Would you`ll say that this is a true or false statement?

Work Gear for Electricians and the Trades
Re: transfomer taps #55780
09/06/05 04:32 PM
09/06/05 04:32 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
I thought they where there to dial in the secondary voltage if the primary voltage consistently runs high or low.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: transfomer taps #55781
09/06/05 05:01 PM
09/06/05 05:01 PM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
Answering off the top of my head. (In this group a good way to lose your head.) I think the answer for the test would be False. The taps are for voltage not angle of phase.
A transformer is rated with a fixed primary voltage which is not always available. that is 480 delivered by the utility may be 470 or 490 volts. If you want 240 on the secondary you would use the taps to get 240 volts. Make Sense ?
Alan--
Looking again I just repeated what Iwire said.

[This message has been edited by Alan Nadon (edited 09-06-2005).]


Alan--
If it was easy, anyone could do it.
Re: transfomer taps #55782
09/06/05 05:49 PM
09/06/05 05:49 PM
J
jtorres  Offline OP
Junior Member
Joined: Sep 2005
Posts: 6
San Antonio, Texas
Thanks guys for the quick response and clearing this up for us.

Re: transfomer taps #55783
09/06/05 08:59 PM
09/06/05 08:59 PM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
For low voltage distribution transformers (eg. 480V delta to 208V/120 wye), is it more common to see the taps on the primary or secondary side?

I was under the impression that taps were often on the primary side, so that the core would not be excessively saturated if the supply voltage was a tad high. But I don't have a large sample of transformers to go by.

-Jon

Re: transfomer taps #55784
09/06/05 09:06 PM
09/06/05 09:06 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Jon

Quote
is it more common to see the taps on the primary or secondary side?


Much more common to see the taps on the front side. [Linked Image]

Sorry.... [Linked Image]

Seroiusly I have not paid that much attention to remember if the taps are primary or secondary.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: transfomer taps #55785
09/06/05 09:28 PM
09/06/05 09:28 PM
H
hypress  Offline
Member
Joined: Jul 2004
Posts: 129
Charleston WV
Taps are on the primary side. If your voltage is low you need to select a lower voltage tap (take some of the primary winding out of the circuit). If your voltage is high you need to select a higher voltage tap (add some primary winding to the circuit) It is just the opposite of what you think you would do . It's all about turns raito. If you have a chance to look at a high voltage transformer like 13200/480V it should have a nameplate with a diagram it will be easy to see what is happining with the primary taps.

Re: transfomer taps #55786
09/07/05 12:42 AM
09/07/05 12:42 AM
F
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
any transformer 35 KVA or larger useally have a primary tap in the front and it will marked 4 points above and 2 points below but some have more than that so double check the nameplate to make sure

i do check transformer lead both " unloaded and loaded to make sure it correct voltage most of my time i set at least one step above the normal voltage by time it loaded up it get to correct level

Merci , Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: transfomer taps #55787
09/07/05 06:52 AM
09/07/05 06:52 AM
J
jtorres  Offline OP
Junior Member
Joined: Sep 2005
Posts: 6
San Antonio, Texas
Taps can also be on the low side. You can have one primary voltage and taps for different out-put voltages. But can we all agree that taps Do Not correct the phase angle of the SECONDARY voltage?

Re: transfomer taps #55788
09/10/05 11:04 PM
09/10/05 11:04 PM
W
WFO  Offline
Member
Joined: Sep 2005
Posts: 202
Cat Spring, TX
Quote:
"But can we all agree that taps Do Not correct the phase angle of the SECONDARY voltage?"

That is correct, taps are for voltage adjustment, NOT phase angle or power factor correction.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Trumpy
Trumpy
SI,New Zealand
Posts: 8,250
Joined: July 2002
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,486 Are you busy
188,051 Re: Forum
177,685 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.031s Queries: 15 (0.005s) Memory: 1.0244 MB (Peak: 1.2005 MB) Zlib enabled. Server Time: 2018-10-20 06:52:11 UTC