#55760 09/05/05 11:32 PM
Joined: Mar 2002
Posts: 125
S
Member
I've been through the code book up and down. I can not find the answer to this question. Someone asked me if it was true that if a 4"sq han more than 3 conduit in it , it would not need support. I have seen boxes like this before. I just can not find it in the book. Any help please. Thanks.

Horizontal Ad
#55761 09/06/05 12:27 AM
Joined: Jul 2004
Posts: 9,992
Likes: 35
G
Member
314.28(E) Raceway Supported Enclosure, Without Devices, Luminaires (Fixtures), or Lampholders. An enclosure that does not contain a device(s) other than splicing devices or support a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 900 mm (3 ft) of the enclosure, or within 450 mm (18 in.) of the enclosure if all conduit entries are on the same side.

Exception: Rigid metal, intermediate metal, or rigid nonmetallic conduit or electrical metallic tubing shall be permitted to support a conduit body of any size, including a conduit body constructed with only one conduit entry, provided the trade size of the conduit body is not larger than the largest trade size of the conduit or electrical metallic tubing.

handbook commentary
Boxes are not permitted to be supported by rigid raceways using locknuts and bushings. Enclosures without devices or luminaires, however, are considered to be adequately supported, provided the conduit is connected to the enclosure by threaded hubs and the threaded conduits enter the box on two or more sides and are supported within 3 ft of the enclosure. A box is not permitted to be supported by a single raceway.

[This message has been edited by gfretwell (edited 09-06-2005).]

[This message has been edited by gfretwell (edited 09-06-2005).]


Greg Fretwell
#55762 09/06/05 06:54 AM
Joined: Mar 2002
Posts: 125
S
Member
I do not know how it overlooked that. Thanks much.

#55763 09/06/05 09:08 AM
Joined: Aug 2003
Posts: 1,374
R
Moderator
I think that code reference was supposed to be 314.23, not 314.28.


Ryan Jackson,
Salt Lake City
#55764 09/06/05 10:38 AM
Joined: Nov 2000
Posts: 2,148
R
Member
For the purposes of this application, does the threaded hub have to be part of the box, or is the use of a product like a Meyres Hub permitted?
Don


Don(resqcapt19)

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,400
Joined: April 2002
Top Posters(30 Days)
BigB 6
Jam85 2
Popular Topics(Views)
329,415 Are you busy
254,315 Re: Forum
236,778 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5