Junior Member
|
I was asked the question what the difference between an "Open Delta Sevice and a Yankee or Y Service" was. I've looked in the code book and asked more than 5 electrician's and haven't gotten a definite answer. I was wondering if anybody out there could help me. I live in South Carolina, don't know if that makes a differance.
|
|
|
Re: Services
#55093
08/13/05 11:17 PM
|
Joined: Jul 2004
Posts: 9,557
Member
|
Wye is where the 3 phases are referenced to a central grounded point, looks like a "Y". That is your normal 208.
Open delta, delta "Vee" etc is a delta that skips one of the transformers. Imagine a triangle where you erased one of the sides. That is typically 240v and they centertap one of the secondaries for the ground. The voltages will be 120/120/208 to ground and 240 between phases. Open delta is a cheap way to serve a place that needs 3 phase and also 120v since it only takes 2 transformers. Balancing the phases can be tricky but if done well it works.
Greg Fretwell
|
|
|
Re: Services
#55094
08/14/05 08:57 AM
|
Joined: May 2005
Posts: 706
Member
|
Ckeck out the Technical Reference section of this site for schematics of different services.
Dave
|
|
|
|
|