ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
dsk 13
Admin 8
doc 3
Recent Posts
Bathroom electrical
by doc. 08/19/17 06:53 AM
electircal ageing test on IPC
by SIAME. 08/15/17 02:43 AM
electrical aging test on IPC
by gfretwell. 08/15/17 12:27 AM
"Line level" audio on Cat 5?
by gfretwell. 08/08/17 10:39 PM
Fire alarm phone lines and color coding
by gfretwell. 08/08/17 10:26 PM
New in the Gallery:
Gallery Test
Popular Topics(Views)
239,983 Are you busy
175,581 Re: Forum
167,831 Need opinion
Who's Online Now
0 registered members (), 61 guests, and 8 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#54597 - 08/02/05 09:37 PM Tap for Transformer  
master66  Offline
Member
Joined: Apr 2002
Posts: 257
Masontown, PA, USA
Is this OK?

In a school, there is a 150 KVA transformer (480V delta Primary / 120/208Y secondary) installed 6" away from a MLO panel.

The MLO panel is fed from the MDP (located in an electrical room on the other side of the building) via a 400A Fused switch.

The transformer is fed from the feed-thru lugs in the MLO panel with 4/0 copper in flex.

The transformer then feeds a 120/208Y panel (6" away) with paralleled 4/0 copper in flex terminating in a 400A main breaker.

Does this meet all requirements of articles 240.21 and 450? (2005 NEC)


Work Gear for Electricians and the Trades

#54598 - 08/03/05 06:01 AM Re: Tap for Transformer  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Sure. [Linked Image]

The primary current of the 150 KVA transformer is about 180 amps.

Table 450.3(B) allows the primary overcurrent protection to be 250% of the primary current when secondary protection is provided.


180 x 2.5 = 450 amps.

On the secondary side we are allowed 125% and we can round up to the next standard size OCP.

The secondary current of a 150 KVA transformer is 416 amps.

They could have gone higher than 400 amps on the secondary side. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#54599 - 08/03/05 06:51 AM Re: Tap for Transformer  
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
How and where does the GEC terminate?


Dnk......



Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7524 MB (Peak: 0.8734 MB) Zlib enabled. Server Time: 2017-08-20 15:41:31 UTC