I'm on a job where a hotel is being converted into an assisted living home. On the plans the engineer calls for 2 225 amp panels to come off one 2.5" run with 4/O from the switchgear. The 4/0 will terminate to a 225 breaker in the switchgear. He has it drawn that taps are made for each panel with a 225 main. Is this common, it's the first time I've seen it drawn like this. Are there any restrictions by doing it this way?
Jesus may have been a capenter,but God was an electrician.Genesis1:3
|
|
|
Re: Two Panels One Run
#54570
08/01/05 07:23 PM
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
The only restriction is the calculated load
You can have as many panels as you want fed from one feeder.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Re: Two Panels One Run
#54571
08/01/05 10:07 PM
|
Joined: May 2003
Posts: 2,876
Member
|
Do it very often... One 42ct with lugs in, and lugs out, to another 42ct through a nipple right next to it.