What are the difference between IMC & RMC. I have an electrical contractor telling me there is no difference. I have always spec'd RMC in an explosion proof area. I know the Code states IMC is legal, But I was always taught RMC was stronger and had better grounding of interferance for control circuits using 4-20ma. I would like to stay with RMC what would be a good argument not to use IMC?
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
IMC is less expensive and can be used in all areas that RMC can be used. I am also told that it is stronger, but I have never read anything on that. IMC also has a bigger cross sectional area and is easier to bend.
I would not install RMC unless I was forced to.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jan 2004
Posts: 615
Member
|
I have always found IMC much stiffer and more difficult to bend. I always opt for RMC because it is easier to bend.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Really? I haven't bent either of them in about 6 years or so, so I might not be remembering properly.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
IMC has a thinner wall, and more tempered/stiffer, not sure why.
RMC is slightly thicker, weighs more, less tempered, but seemingly about the same to bend. Costs a penny more.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
I agree that IMC is much stiffer and harder to bend and thead than RMC. I have also seen problems with the IMC breaking at the threads on the 1/2 and 3/4" size. This is caused by the reduced wall thickness of this conduit. There is very little strength left after you cut the threads. Don
Don(resqcapt19)
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
I used a fair amount of IMC and GRC in hazardous locations including 4-20 mA control circuits and VFDs. Never noticed a diffrence in EMI or RFI problems in one over the other. Although lighter in weight the IMC was indeed harder to bend, and keeping the shoe tight against the pipe for an accurate radius was difficult even at the 3/4" size. I would avoid using it for hand bending.
|
|
|
|
Joined: Jul 2004
Posts: 10,004 Likes: 36
Member
|
From an RF standpoint a wrap of properly grounded metal window screen is as effective as RMC. The difference is physical protection.
Greg Fretwell
|
|
|
|
Joined: Jun 2001
Posts: 21
OP
Member
|
Thanks for the feed back.
|
|
|
|
Joined: Jul 2002
Posts: 680
Member
|
I prefer working with IMC, lighter and easier to bend IMHO. Never had a problem with it breaking underground and Maine frost can break anything. My suppliers don't stock it anymore though so I use RMC all the time now anyway. What are people paying for 3/4 rigid, last time I checked it was 17 bucks a stick up here??
|
|
|