Uli,
If this is in relation to an installation in Ontario, Canada follow Section 75 for related info.
75-244 Pole Spans and Framing
(1) Poles used in secondary lines shall be placed not more than 40 m apart.
(2) Subject to Subrule (3), poles used in primary lines shall be placed not more than 90 m apart.
(3) Poles used in primary lines shall be framed as per following specifications:
Specification 9 - Primary, 1Ø, 2.4 to 8 kV, Maximum span 90 m.
Specification 10 - Primary, 1Ø, 2.4 to 16 kV, Maximum span 90 m.
Specification 11 - Primary, 3Ø, 2.4/4.16 to 8.0/13.8 kV.
Specification 12 - Primary, 3Ø, 2.4/4.16 to 16/27.6 kV.
Specification 13 - Primary, 3Ø, Line Angles 4°-90°, 2.4/4.16 to 16/27.6 kV.
Specification 14 - Primary, 3Ø, Crossarm, 2.4/4.16 to 16/27.6 kV.
Specification 15 - Primary, 3Ø, Underbuilt, 2.4/4.16 to 16/27.6 kV.
Specification 16 - Primary, 3Ø, 44kV.
Specification 17 - Primary, 3Ø, Line Angles 4°-90°, 44 kV.
Specification 18 - Primary, 3Ø, Crossarm, 44 kV.
Tony Moscioni
Electrical Inspector
© Electrical Safety Authority