Has any one seen or used "High Density Polyethylene Conduit? I just came acrost it in the code and know nothing more then that.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I'll bet you've seen big rolls of it on the back of utility trucks before. Probably blue or red.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
Carlons web site has pdf info
|
|
|
|
Joined: Dec 2004
Posts: 329
Member
|
We use it under raised floors in some of our systems we build. While I have not personally worked with it, it seems pretty durable.
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
353.12 appears to limit the use of HDPE to exterior installations only??
Charlie
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
We used to use it pretty regularly in residential to provide a chase for tv cable and phone cable to be run underground from the street box to the demark for the house. Both the cable co. and the phone co. now insist on a min 1" pvc conduit for the same job.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Please read Charlie's reply again. You cannot use this wiring method at all in the 2002 NEC, and in the 2005 it must be outdoors and concelaed.
Ryan Jackson, Salt Lake City
|
|
|