TRAVELERS THROUGH FIXTURES #52259 05/23/05 09:09 PM
Joined: Jul 2004
Posts: 129
H
hypress Offline OP
Member
Can 3way switch travelers run through fluorescent fixtures. I have always been under the impression that the only wiring that can be in fixtures is the wiring that powers the row of fixtures and the travelers must be in a seperate raceway. THANKS HYPRESS

Work Gear for Electricians and the Trades
Re: TRAVELERS THROUGH FIXTURES #52260 05/23/05 09:16 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Hypress, I'm not sure if this addresses your question, but you might check out 410.31 and 410.32 and see if these article sections may apply.

In reality, the travelers are extensions of the switch leg.

Roger

[This message has been edited by Roger (edited 05-23-2005).]

Re: TRAVELERS THROUGH FIXTURES #52261 05/23/05 09:51 PM
Joined: Jul 2004
Posts: 9,541
G
gfretwell Offline
Member
Does this 3way loop control the fixtures in question? If so I say it is OK.
I wouldn't allow conductors from another circuit.


Greg Fretwell
Re: TRAVELERS THROUGH FIXTURES #52262 05/24/05 05:48 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Quote
Does this 3way loop control the fixtures in question? If so I say it is OK.
I wouldn't allow conductors from another circuit.

As Roger pointed out 410.31 and 410.32 are the requirements

If the fixture is listed as a raceway (410.31) which most fluorescent strips are you may treat it as just another raceway.

You want to run a 480 volt 100 amp 3 phase feeder through raceway listed fixtures you may.

If the fixture is not listed as a raceway then we have to follow 410.32.

Quote
410.32 Wiring Supplying Luminaires (Fixtures) Connected Together.
Luminaires (fixtures) designed for end-to-end connection to form a continuous assembly, or luminaires (fixtures) connected together by recognized wiring methods, shall be permitted to contain the conductors of a 2-wire branch circuit, or one multiwire branch circuit, supplying the connected luminaires (fixtures) and need not be listed as a raceway. One additional 2-wire branch circuit separately supplying one or more of the connected luminaires (fixtures) shall also be permitted.

The travelers are part of the lighting circuit supplying the fixture.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: TRAVELERS THROUGH FIXTURES #52263 05/24/05 11:07 AM
Joined: Jul 2004
Posts: 9,541
G
gfretwell Offline
Member
How many are listed as a raceway?


Greg Fretwell
Re: TRAVELERS THROUGH FIXTURES #52264 05/24/05 11:35 AM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
Glenn, many industrial strip fixtures are. They are even refered to
as "channel/wireway" in the information that accompanies them.

Roger

Re: TRAVELERS THROUGH FIXTURES #52265 05/24/05 02:16 PM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
i will like to pass the word with the raceway in flourscent lumiaires you have to be carefull with wire fill espcally near the ballast area they do kick up a bit of heat.

just make sure you read 410.32 very carefully there and watch out the space requirements there

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: TRAVELERS THROUGH FIXTURES #52266 05/24/05 09:22 PM
Joined: Jul 2004
Posts: 9,541
G
gfretwell Offline
Member
Thanks Roger, I guess I never saw them used that way.
It sure reinforces "qualified personel only".

It would be easy to assume that if you tripped the breaker and the lights went out that the conductors inside would be deenergized. Horrible scenarios abound from there.


Greg Fretwell

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,953 Are you busy
205,843 Re: Forum
193,921 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3