ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by tortuga - 03/18/24 08:39 PM
240V only in a home and NEC?
by tortuga - 03/18/24 04:29 PM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
Test Post
by sabrown - 03/06/24 05:29 PM
Solar PV Wiring Errors
by renosteinke - 03/02/24 09:12 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 94 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#51704 05/08/05 05:52 PM
Joined: Feb 2001
Posts: 32
G
Member
Talk to the city. I am sure they mean in each unit all smokes shall be interconnected. Not all unit's interconnected together. Look at any new multi family building. Each unit supplies the power for the unit's interconnected smoke detectors.

#51705 05/08/05 07:08 PM
Joined: Jun 2004
Posts: 613
S
Member
Hey guys...hows it going, been on vacation [Linked Image]

I agree with Active 1 and his statement regarding the rules pertaining to hard wired smoke detectors that are not supervised. NFPA 72 1999 edition, section 8-1.4.4 specifically limits the number to 18 initiating devices (of which 12 can be smoke detectors)

Wirenuttt...it is not practical to interconnect the smoke detectors of one dwelling unit to another dwelling unit.Every time the occupant of one unit overcooks something in the kitchen, other people in the building would be be disturbed by the nuisance alarm.

Electricmanscott pointed out how Massachusetts requires a heat detector to be installed not more than 6 feet from a exit in each seperate dwelling unit of a multifamily building. This heat detector would be connected to the common area fire detection system which is connected to the public electric supply.This way when there is a real fire in any unit hopefully the heat detector will set off the buildings common fire alarm system.

Larry Fine...I haven't ever seen a 120volt hard wired smoke detector that allows more than 12 smokes to be interconnected. Sure the front of the box might say 20 detectors interconnected...but read those instructions carefully and you will see that they all limit the number of smokes to 12 maximum. This is because of the rules in NFPA 72...which is adopted by most local goverments.

shortcircuit

#51706 05/09/05 09:48 PM
Joined: Nov 2002
Posts: 267
W
Member
Thanks everyone for your replies. I agree with all of you. It didn't make sense when the electrician called me on it. I had mentioned to him to check with the locasl F.D.. I don't know who in the city was requiring this but it sounds like he's way off.

Page 2 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5