researcher in electrophysiology lab wants an isolated dedicated ground, separate from the building ground system. He wants "to connect his equipment to this isolated ground system, thereby preventing ground loops and minimizing the electrical/magnetic fields that result from ground loops"
If this Grounding System is not physically bonded to the Power System, of which the Equipment is driven from, there WILL be extreme levels of noise (and other fun issues), because this is:
"A Great Method To Create Ground Loops!" If you want to drive a rod or a few rods (or create another type of Electrode System) locally to this Lab, that's OK - just include them in the complete Scheme.
The "Complete Scheme" would be a sufficiently sized Eq. Grounding Conductor, ran from the Lab, to the Main Service Equipment (or "convenient" "effectively Ground Bonded" item - as pointed out in Article 250).
If terminated at the Service Equipment, land to the Grounded Conductor bus.
If terminated elsewhere, well - land it via an approved and mechanically solid termination means.
At the Lab, Bond the new Ground Rods (or other acceptable Electrode System) to this Equipment Grounding Conductor.
(by "Bonding" I mean to mechanically and electrically connect the GES to the newly ran EGC).
Without a solid bonding between the two Grounding Electrode Systems, the only connection is via a realitively high Impedance circuit - the Earth (Dirt, Soil, Actual "Ground", etc.).
Place a High Z (Impedance) load across any Power Supply, and the result will be current flowing through the circuit / load!
Try explaining this to the guy in the Lab, so there is no question as to how the grounding scheme should be done.
Exception to this whole thing:
If the Lab Equipment is driven from a Local Isolation (1:1) Transformer - or some other SDS means, then the Primary side feeders should (hopefully) include an EGC for bonding the Transformer's enclosure.
Along with that, there "Should" be a Local GES for the Transformer(s)' Secondary side output.
The GES would be Bonded to the Secondary side (typically at "X0") for a Grounded AC Power System, or to the enclosures only (not to the Electrical System) if the output is an Ungrounded System.
Let us know what the outcome is!
Scott35