Joined: Sep 2004
Posts: 174
OP
Member
|
I'm doing a rehab job turning a old hotel into a retirement center and there is alot of exsisting openings that will no longer be in use. Does the NEC make mention of abandoned boxes,runs,ect. I wondering if I need to remove these completely to be code complient or if I can just demo the run that feeds these and let them mud over them?
Jesus may have been a capenter,but God was an electrician.Genesis1:3
|
|
|
|
Joined: Aug 2004
Posts: 34
Member
|
I am almost possitive there is a section that you have to remove any unused old conduit, box, equipment and conductors. I remember it from the 2002 NEC code class. I am trying to look it up for you.
|
|
|
|
Joined: Dec 2003
Posts: 886
Member
|
No, only low voltage. This has been a hot topic for some who would like to see the code changed to require all abandoned wiring and materials removed.
The reason low voltage wiring must be removed is because it adds to the fire/smoke load. Tough to argue that basis when you are talking about pipe and boxes. About the only thing it could be is a workmanship issue which the code does not strictly define.
-Hal
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
On some of the Air Force installations I've been on, any abandoned boxes/conduits were labeled "ABNDN"
I guess one could tag any wires the same way...
Stupid should be painful.
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Remember also that this rule for low voltage applies only to the accessible portions of such cables. That does not include cables in raceways, by definition.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Mar 2005
Posts: 53
Member
|
anyone know the art.# that says a wire can not be abandoned? I myself when do abandon a wire crimp all the the conductors together (in my area romex)(especially the bare ground)and mark it spare, on both ends. in case some one else down the road decides to hook it back up, with all the conductors tied together should trip a breaker and make who ever do some more investigation. Of course I do agree that removing the abandoned cable is the best choice,and if wires in conduit no problem, but then there's them times!!!!
[This message has been edited by highvoltageguy (edited 04-21-2005).]
|
|
|
|
Joined: Jan 2005
Posts: 354
Member
|
Oh look ... here's some abandoned cable. It's running from one room to the next inside a conduit. It's been snipped off on each end and is connected to nothing.
Q: is this high voltage? low voltage? or no voltage?
|
|
|
|
Joined: Jul 2004
Posts: 9,988 Likes: 35
Member
|
You never abandon wire. You tape it back on itself and label it "spare".
Greg Fretwell
|
|
|
|
Joined: Aug 2001
Posts: 335
Member
|
I had this discussion with my local inspector about 6 months back. His (our local county's) interpretation was to either cut the wires off where they enter the boxes or cap them off within the boxes. As long as they were not left bare ended for the next guy to accidently hook up they (AHJ) had no problem. It seemed reasonable and fair to me so we capped them and left them.
|
|
|
Posts: 28
Joined: February 2011
|
|
|
|
|