#50563 04/06/05 12:38 AM
Joined: Jun 2004
Posts: 176
P
Member
I want to know what the proper way is to install fiberglass insulation around 1) Wires running along/thru studs, 2) Around Outlet Boxes, and 3) Around Light fixtures, where it will be hot. (All NM-B, no conduits or ac). (I know that nobody is liable for any advice blah blah blah legal stuff here blah blah blah)

#50564 04/06/05 07:39 PM
Joined: Jan 2002
Posts: 1,457
E
Member
You might want to ask that in the insulation forum. [Linked Image]

#50565 04/06/05 09:12 PM
Joined: Dec 2004
Posts: 209
H
Member
In VA. our inspectors require us to remove the paper backing within 6" of a recessed type IC fixture. The fiberglass batt can be snug to the fixture. There doesn't seem to be any other problems around boxes or NM-B. We do tuck it behind the box to satisfy the energy code and help prevent drafts thru the outlets.

#50566 04/06/05 09:29 PM
Joined: Dec 2003
Posts: 886
H
Member
The important thing with fiberglass insulation is that you don't want to compress it. If you do the R value will be less where it is compressed.

With that in mind a good insulation installer will do a knife cut partially through the batt from the backside to put a horizontal cable in the center of the insulation without compressing it. The same can be done for vertical runs only the insulation can be split with your fingers to accommodate the cable.

I like to see the space behind a box (between the back of the box and the sheathing) filled with uncompressed insulation. You again would split the insulation with your fingers, slide a layer behind the box then cut the front layer away around the box. I think that the thin uncompressed layer behind the box has a higher R value than the whole thickness shoved in there.

Light fixtures in insulation should be type IC so they can (and should) be completely covered following the same rules I gave above if applicable.

-Hal


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Alan Belson
Alan Belson
Mayenne N. France
Posts: 1,803
Joined: March 2005
Top Posters(30 Days)
BigB 3
triple 2
Popular Topics(Views)
305,035 Are you busy
233,456 Re: Forum
218,144 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5