ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
Joined: Oct 2004
Posts: 72
B
Member
George.
thanks for your post.
ya the length of conductor is not in the ground. It runs through the house to the water pipe and rods.

ya the code is silent on the lenth of conductor but not the size.
So if the code is silent on the length how can the AHJ infoce it?

Joined: Feb 2005
Posts: 44
B
Member
That is why they call it AHJ, because they have the last word on it. Hell there are parts of the country still working on 1999 code because their AHJ didn't adopt the 2002.

Joined: Jun 2001
Posts: 642
N
Member
I would ask the AHJ to give me a quote reference for the NEC bieng enforced in your area. Unless there is a legally adopted local code requirement, he cannot ask for some thing that is not code.
As was noted above the ground rods do not help the circuit breaker trip in a fault condition.


ed
Joined: Oct 2004
Posts: 72
B
Member
why don't ground rods help?
if it's less then 25 ohms it's all good right.
if you drive two no need to test for 25
and that could meen you still might have more?

Joined: Jan 2002
Posts: 163
D
Member
bucketman -

"why don't ground rods help?"...because ground rods are for directing lightning strikes and high voltage line surges (Poco problems) to ground...this current is not part of your circuit wiring and thus does not pass through your circuit breaker.

Another point - if you look at Table 8, it shows the resistance on a #4 conductor over a distant of 1,000 feet to be .508! ....that's .0508 for 100 ft....do the arithmetic...this resistance is so low as to have NO affect on a lightning strike going to earth.