0 members (), 368 guests, and 26 robots.
#48733 02/19/05 04:50 PM
The answer is above. I think iwire's post is the answer you were actually seeking.
Think about what is connected to it, and forget about the number of breakers for a minute. If you've got 21 amps on each leg, you will have 21 amps on each leg, period.
Now, split it up however you'd like.
4-15 amp 1 polebreakers with 10.5 amps on each of them.
42-20 amp breakers with 1 amp on each of them.
The panel still sees a load of 21 amps per leg.
Get it? It's the LOAD, not the # of breakers.
[This message has been edited by electure (edited 02-19-2005).]
#48734 02/19/05 05:06 PM
the amount of breakers has nothing to do with connected load.
Think about it this way, you have a 20 amp single pole circuit feeding receptacles in any given room, you put a recording amp meter on it for an extended period of time and see the peak is 7 amps with an average of 2 amps over this period. This would probably be exaggerated for many circuits, so the face value of an OCPD is not really relative when computing a service or panel feeder.
Roger
#48735 02/19/05 05:09 PM
Hello Electure, I appologize, we must have been typing at the same time. [Linked Image]
Roger
#48736 02/19/05 06:20 PM
That is the concept behind that pesky term "load diversity". Not all loads will be operating fully and simultaneously. This means you can put (40) 20 amp breakers in a 200 amp, 40 ckt panel.
#48737 02/19/05 10:19 PM
what you seem to be trying to do is a load calculation.
exsample in
