#48733 02/19/05 04:50 PM
Joined: Dec 2000
Posts: 4,294
Member
The answer is above. I think iwire's post is the answer you were actually seeking.

Think about what is connected to it, and forget about the number of breakers for a minute. If you've got 21 amps on each leg, you will have 21 amps on each leg, period.

Now, split it up however you'd like.
4-15 amp 1 polebreakers with 10.5 amps on each of them.
42-20 amp breakers with 1 amp on each of them.

The panel still sees a load of 21 amps per leg.

Get it? It's the LOAD, not the # of breakers.

[This message has been edited by electure (edited 02-19-2005).]

#48734 02/19/05 05:06 PM
Joined: May 2002
Posts: 1,716
R
Member
the amount of breakers has nothing to do with connected load.

Think about it this way, you have a 20 amp single pole circuit feeding receptacles in any given room, you put a recording amp meter on it for an extended period of time and see the peak is 7 amps with an average of 2 amps over this period. This would probably be exaggerated for many circuits, so the face value of an OCPD is not really relative when computing a service or panel feeder.

Roger

#48735 02/19/05 05:09 PM
Joined: May 2002
Posts: 1,716
R
Member
Hello Electure, I appologize, we must have been typing at the same time. [Linked Image]

Roger

#48736 02/19/05 06:20 PM
Joined: Mar 2001
Posts: 2,056
R
Member
That is the concept behind that pesky term "load diversity". Not all loads will be operating fully and simultaneously. This means you can put (40) 20 amp breakers in a 200 amp, 40 ckt panel.

#48737 02/19/05 10:19 PM
Joined: Oct 2004
Posts: 72
B
Member
what you seem to be trying to do is a load calculation.
exsample in