Connecting two ground rods #48006 02/01/05 08:19 PM
Joined: Mar 2004
Posts: 55
E
eswets Offline OP
Member
I did a service the other day, and the inspector wants me to install a second ground rod 6' away even though it is less than 25ohms. Im not going to argue, b/c I will get paid to do it, but I need to know how to connect the other ground rod. Most other EC I'ved talked to never had to do this. Can I just run direct burial wire in the ground from the 1st G.R. to the second or each from the ground lug?
Thanks

Work Gear for Electricians and the Trades
Re: Connecting two ground rods #48007 02/01/05 08:30 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
You must have real good soil conductivity to get below 25 ohms with one rod.

I generally just run a continuous GEC from the panel, to one rod, then to the next rod.Leave the wire on the surface, and bury it in a shallow trench after inspection....

Re: Connecting two ground rods #48008 02/01/05 08:31 PM
Joined: Jan 2005
Posts: 5,316
renosteinke Offline
Cat Servant
Member
I've done this several times. I connect rod #2 to rod #1 with one length of wire & connectors (all of ours should be exposed, in pipe here). Another wire connects rod #1 to the panel.

Re: Connecting two ground rods #48009 02/01/05 09:27 PM
Joined: Aug 2003
Posts: 99
richard Offline
Member
you should check with the poco or inspector in your area. We had to have one wire from each rod to the meter base.

Re: Connecting two ground rods #48010 02/01/05 09:44 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
If your under the NEC and it is less than 25 ohms why are you still going to do it? Anyway just dig a small trench between the rods and run the wire between them. Connect to each rod and you are done. Until the inspector comes up with something else he would like you to do. [Linked Image]

Re: Connecting two ground rods #48011 02/02/05 08:07 AM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
How did you test it to find that it is less than 25 ohms?
Don


Don(resqcapt19)
Re: Connecting two ground rods #48012 02/02/05 03:53 PM
Joined: May 2002
Posts: 10
B
Belgariad Offline
New Member
All inspectors in my area that I've dealt with require two ground rods. Also I have failed for not having a continuous wire from meter base to both rods.

Re: Connecting two ground rods #48013 02/02/05 03:54 PM
Joined: Jul 2002
Posts: 8,346
Trumpy Offline
Member
Don,
Quote
How did you test it to find that it is less than 25 ohms?
Good point. [Linked Image]
eswets,
There are ready made clamps for this very thing.
Personally I'd just use a single heavy wire between the two rods.

Re: Connecting two ground rods #48014 02/02/05 05:46 PM
Joined: Nov 2004
Posts: 56
D
detubbs Offline
Member
we do one continuous run of bare copper #6 here in our area. one end in the panel one rod just outside the building and one a ground rod length away. this is pretty much standard in our area. our inspectors and poco's want it this way if possible, plus it's easy and fewer house penetrations to do it this way when your installing or replacing a service.


Scott
Re: Connecting two ground rods #48015 02/02/05 06:47 PM
Joined: Jan 2005
Posts: 315
L
luckyshadow Offline
Member
The county I live in in Maryland has been requiring 2 rods for last couple years now.
When I wired my house I ran one # 6 out of the panel through the clamp on rod # 1 then over to rod # 2. One wire two rods . Now I hear the county wants footer gronds instead of rods.

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,057 Are you busy
205,954 Re: Forum
194,003 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3