Smoke Detectors #47351 01/14/05 01:19 PM
Joined: May 2003
Posts: 1,154
dougwells Offline OP
Member
Got a call today that The Smoke Detectors were activating during the night.There is 4 of them and it seems that this has just started with the cold Temperatures .They are 8 years old, all i could was suggest was to have them replaced.

Work Gear for Electricians and the Trades
Re: Smoke Detectors #47352 01/14/05 01:53 PM
Joined: Dec 2003
Posts: 886
H
hbiss Offline
Member
Time to replace them anyway and that will probably take care of the problem. They get dirt and insects inside them, particulary spiders for some reason.

-Hal

Re: Smoke Detectors #47353 01/14/05 02:13 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline
Member
They're supposed to be replaced after 10 years anyway, so this is a good opportunity. The last ones I had go off was with a cleaning lady using a vacuum. It was throwing off dust because the bag was full.

Dave

Re: Smoke Detectors #47354 01/14/05 04:48 PM
Joined: Jan 2004
Posts: 615
J
Jps1006 Offline
Member
What you could have is a problem with codensation. If it's conduit, your (his) warm moist house air travelling through the cold attic will cause water to form in the pipe and drip down. If it's romex, I don't know, but I wouldn't rule out condesation.

I have seen this many times where the water shorts out the smoke. That's why I never run conduit straight up out of a wall or ceiling box and extend it into open attic. Always follow the contour of the insulation for as long as you can. If you have to up to an attic light, put a few 90's before you fly. This way any condensation will have a chance to re-evaporate as it warms back up.

Re: Smoke Detectors #47355 01/14/05 10:31 PM
Joined: Dec 2001
Posts: 444
S
Sandro Offline
Member
I've seen this feature on some models of smoke detectors...the detector's light flashes to alert the HO which detector went off first.

Why replace all of them if only one is faulty?

Re: Smoke Detectors #47356 01/15/05 12:05 AM
Joined: May 2004
Posts: 697
D
Dave55 Offline
Member
That's interesting, Sandro. Do you know what model?

Dave

Re: Smoke Detectors #47357 01/15/05 06:15 PM
Joined: Jun 2003
Posts: 1,143
D
DougW Offline
Member
+1 for the 'condensation trip' advice. Check the detector on the cathedral ceiling first. (longest run / thinnest insulation)

Re: Smoke Detectors #47358 01/15/05 06:32 PM
Joined: Oct 2000
Posts: 3,930
Bill Addiss Offline
Member
Dave,

The Firex Smokes will tell you which one is going off.
Quote

LED INDICATORS
This smoke alarm features an LED indicator which can be seen through the Push-to-Test button. The LED indicates the following:

Blinks once a minute — indicating normal operation.

Blinks once a second — smoke alarm senses smoke and simultaneously sounds an audible alarm.

Blinks once approximately every 10 seconds — False Alarm Control™ (FAC) feature activated (model GC only).

OFF — another smoke alarm in the (Interconnected system only): network has sensed smoke and is signalling this alarm.
See Page 5 of: http://www.icca.invensys.com/manuals/firex/110-427G.pdf

Bill

[This message has been edited by Bill Addiss (edited 01-15-2005).]


Bill
Re: Smoke Detectors #47359 01/15/05 06:55 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline
Member
Thanks Bill!

Dave

Re: Smoke Detectors #47360 01/16/05 07:33 PM
Joined: Nov 2002
Posts: 267
W
Wirenuttt Offline
Member
I use to tell the H.O to vaccum the smokes once a month, specially if they had a hot air system. Also, for a little more investment, install the photo instead of the ionization type. Photo is less nuisance alarm and I always worried that they would unplug the ION types and forget they were unplugged.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
sparky 10
Popular Topics(Views)
259,739 Are you busy
195,069 Re: Forum
184,477 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3