Generator testing with bldg. load #46472 12/23/04 05:52 PM
Joined: Jul 2004
Posts: 136
C
cgw Offline OP
Member
Apparently nursing homes are required to test thier standby generators by transfering the building load to the generator. Has anyone seen any problems associated with this monthly switch throwing??
(e.g. voltage spikes or dips)

Work Gear for Electricians and the Trades
Re: Generator testing with bldg. load #46473 12/23/04 06:19 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
It is more than a dip, it is an interruption.

You will want to make sure any items like PCs are either off or on UPS.

I don't believe you will see see spikes or other issues as the switch won't transfer until the generator is running smoothly.

I am assuming a modern automatic transfer switch.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Generator testing with bldg. load #46474 12/23/04 08:04 PM
Joined: Aug 2004
Posts: 186
N
NJ Wireman Offline
Member
we have a gen. system in our fire station that we test monthly, we kick it over with everything on pc tv's what ever happens to be on at the time. Never had a problem in 11 years. let me tell ya you hate to be the guy to test it when that thing throws itself its loud.

[This message has been edited by NJ Wireman (edited 12-23-2004).]

Re: Generator testing with bldg. load #46475 12/23/04 08:12 PM
Joined: Dec 2003
Posts: 84
S
slumlordworker Offline
Member
I worked as maintenance supervisor for over a year at a nursing home and I never had any problems with our generator.

we were required to run ours once a week and throw or trip the switch once a month. I rigged a meter up to the panel that it feed to get voltage measurements.

all was fine til we had an ice storm and that poor thing ran for about 9 hours than finaly it gave the ghost. talking about a erious issue when it is 25 outside and your healthcare provider has no power or heat at all that was a long and intresting night to say the least

Re: Generator testing with bldg. load #46476 12/23/04 11:15 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
Many health care facilities specify a transfer switch that has the ability to sync and briefly parallel with the utility so there is no outage for the required testing.
Don


Don(resqcapt19)

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles, CA
Posts: 349
Joined: April 2004
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,026 Are you busy
205,035 Re: Forum
193,143 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3