#46345 12/19/04 08:36 AM
AndyP Offline OP
What is the ampacity of the wire in #11 if it was installed to feed Light poles?
I look in Article 310.16 but I'm just confused.
lol man I'm tired. #11 meaning THHN 8 awg
[This message has been edited by AndyP (edited 12-19-2004).]
#46346 12/19/04 08:43 AM
"What is the ampacity of the wire in #11 if it was installed to feed Light poles?"
Whats #11 refer to?
#46347 12/19/04 08:56 AM
AndyP Offline OP
Never mind I think it's 55a
#46348 12/19/04 09:09 AM
Generally conductors below 100amp are rated according to the 60degree column of 310.16.
You must rate the wire to the lowest value of any component in the circuit. The degree rating of the breaker, and any devices, lugs, or equipment, have to be taken into concideration.
8 copper = 40amps for 3 or less conductors.
You have to derate if you have more than three conductors or have ambient temperatures greater than 86 degrees F.
To derate the wire use the 90 degree column if using thhn/thwn.
[This message has been edited by russ m (edited 12-19-2004).]
#46349 12/19/04 09:15 AM
while you may use the 90 degree column for derating, (use what ever column the wire is rated for) you still have to use the lower of the two values for your conductor ampacity. Meaning the the lower of the two, (1)60 degree column or (2)the derated 90 degree wire.
#46350 12/19/04 09:19 AM
AndyP Offline OP
Thanks
#46351 12/19/04 09:19 AM
Andy it is very unlikely you can use the 90 C column which lists 8 AWG @ 55 amps.
You may very well be able to use the 75 C column if the terminations you are using are rated 75 C. At 75 C 8 AWG CU is rated 50 amps.
#46352 12/19/04 09:28 AM
It might be helpfull for you to look at article 110.14(C)
I had to edit the article number
#46353 12/19/04 11:13 AM