NEC Help #46345
12/19/04 09:36 AM
12/19/04 09:36 AM
A
AndyP  Offline OP
Member
Joined: Aug 2004
Posts: 20
What is the ampacity of the wire in #11 if it was installed to feed Light poles?

I look in Article 310.16 but I'm just confused.

lol man I'm tired. #11 meaning THHN 8 awg

[This message has been edited by AndyP (edited 12-19-2004).]

[This message has been edited by AndyP (edited 12-19-2004).]

Work Gear for Electricians and the Trades
Re: NEC Help #46346
12/19/04 09:43 AM
12/19/04 09:43 AM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
"What is the ampacity of the wire in #11 if it was installed to feed Light poles?"

Whats #11 refer to?

Re: NEC Help #46347
12/19/04 09:56 AM
12/19/04 09:56 AM
A
AndyP  Offline OP
Member
Joined: Aug 2004
Posts: 20
Never mind I think it's 55a

Re: NEC Help #46348
12/19/04 10:09 AM
12/19/04 10:09 AM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
Generally conductors below 100amp are rated according to the 60degree column of 310.16.

You must rate the wire to the lowest value of any component in the circuit. The degree rating of the breaker, and any devices, lugs, or equipment, have to be taken into concideration.

8 copper = 40amps for 3 or less conductors.
You have to derate if you have more than three conductors or have ambient temperatures greater than 86 degrees F.

To derate the wire use the 90 degree column if using thhn/thwn.

[This message has been edited by russ m (edited 12-19-2004).]

Re: NEC Help #46349
12/19/04 10:15 AM
12/19/04 10:15 AM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
while you may use the 90 degree column for derating, (use what ever column the wire is rated for) you still have to use the lower of the two values for your conductor ampacity. Meaning the the lower of the two, (1)60 degree column or (2)the derated 90 degree wire.

[This message has been edited by russ m (edited 12-19-2004).]

Re: NEC Help #46350
12/19/04 10:19 AM
12/19/04 10:19 AM
A
AndyP  Offline OP
Member
Joined: Aug 2004
Posts: 20
Thanks

Re: NEC Help #46351
12/19/04 10:19 AM
12/19/04 10:19 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Andy it is very unlikely you can use the 90 C column which lists 8 AWG @ 55 amps.

You may very well be able to use the 75 C column if the terminations you are using are rated 75 C. At 75 C 8 AWG CU is rated 50 amps.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: NEC Help #46352
12/19/04 10:28 AM
12/19/04 10:28 AM
R
russ m  Offline
Member
Joined: Feb 2003
Posts: 169
Burbank,IL,USA
It might be helpfull for you to look at article 110.14(C)

I had to edit the article number

[This message has been edited by russ m (edited 12-19-2004).]

[This message has been edited by russ m (edited 12-19-2004).]

Re: NEC Help #46353
12/19/04 12:13 PM
12/19/04 12:13 PM
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,545
NY, USA


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,905
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,445 Are you busy
190,685 Re: Forum
180,402 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.030s Queries: 14 (0.004s) Memory: 0.9996 MB (Peak: 1.1664 MB) Zlib enabled. Server Time: 2019-04-19 09:16:33 UTC