MDP for Sub Division #45494 11/30/04 06:34 PM
Joined: Feb 2004
Posts: 494
M
mustangelectric Offline OP
Member
Hi,
I am setting up a design for a all electric subdivision where the owner is paying all the utilities and installing his own water treatment facility. There is also permanent site lighting that will be installed (Stainless Light Poles) throughout the subdivision.

Each residence will have a 100A main breaker in a NEMA 3R panel mounted on the exterior wall and there are 220 residences in the subdivision.

Wouldn't this be best acheived with primary metering, switchboard, and pad mounted transformers that will be located throughout the subdivision to feed the residences and the area lighting.

What is the best setup for this type of installation? A primary metered MDP with 480 VAC feeders to the transformers and service laterals from the pedastals to the residence?

I was thinking a Switchboard with high voltage breakers feeding the transformers?

What is the most common type of installation for this type of setup?

I would apprecite any suggestions.

Thanks for any replies.

-regards

Mustang

Work Gear for Electricians and the Trades
Re: MDP for Sub Division #45495 11/30/04 08:24 PM
Joined: Feb 2004
Posts: 75
S
scameron81 Offline
Member
I have only seen a setup like your talking about once before. It wasn't a subdivision but a large resort. The Poco metered the 12KV and then set a 12kv/4160 transformer which was then distrubuted to the different areas where they placed transformers for each building.

IMHO based on the size of the subdivision It seems like 480VAC distribution wouldn't quite be enough to power the subdivision without worrying about voltage drop issues or some pretty good sized feeders.

I hope I have been at least a little help


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,205 Are you busy
206,090 Re: Forum
194,093 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3