Reducing conduit size #44874
11/14/04 06:26 PM
11/14/04 06:26 PM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
An inspector told me I could not reduce the size of conduit in a run except at the termination. The contractor ran a 2" PVC underground. At grade level I installed a Female Adaptor and a 2"x1" reducing bushing.
I then ran 1" sealtight to a small panel in a piece of equipment. The circuit was 3 #8,
1#10 Grd. The total length of the entire run was only about 12'. He said "It's somewhere in the code book". Can someone save me a hassle and let me know where to find that one?
Thanks

Work Gear for Electricians and the Trades
Re: Reducing conduit size #44875
11/14/04 06:30 PM
11/14/04 06:30 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
The inspector can not find it because that rule does not exist.

While most times it is not a great idea it is not a code violation.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Reducing conduit size #44876
11/14/04 09:53 PM
11/14/04 09:53 PM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
I agree. I have never run across that rule either. By the way, that was the same inspector I mentioned in another thread I started a while back. "Inspectors who are
#+%*&".

Re: Reducing conduit size #44877
11/15/04 09:57 AM
11/15/04 09:57 AM
S
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 329
Bruceton Mills, WV
Try my classic response: "Thanks for pointing that out. When you get back to the office would you call me and tell me the code section so I can read up on it. I'd hate to get caught in the same mistake twice."

It usually works; plus he's at the other end of the phone now and it's easier for him to say he'll let it go when he's not face to face.

Re: Reducing conduit size #44878
11/16/04 05:24 PM
11/16/04 05:24 PM
D
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
As others have said - he's talking out of his errr, pants...

As long as your within limits for conductor fill (which you are) there's nothing in th Code that prohibits it.

Re: Reducing conduit size #44879
11/16/04 09:28 PM
11/16/04 09:28 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Tell the inspector he/she is looking from the wrong end, and that in reallity, you increased the conduit size and did not reduce it. [Linked Image]

I know, and I apologize. [Linked Image] [Linked Image]

Roger

Re: Reducing conduit size #44880
11/19/04 02:53 AM
11/19/04 02:53 AM
W
wewire2  Offline OP
Member
Joined: Nov 2002
Posts: 244
California
I just got back from an out of town job
(3 days). I got called on one thing. No plastic bushings on 3" PVC Terminal adaptors.
The contractor oversized the underground conduit from plan specs from 2" to 3". The pull was 2 #1 and 1#8 Grd. So as you can can imagine there are three dinkey little wires coming out of a huge conduit, not even touching the edges. The inspector made me tear everything apart to install bushings. I believe in bell ends for feeding but do you always use bushings on PVC and is this a fair call?

Re: Reducing conduit size #44881
11/19/04 03:38 AM
11/19/04 03:38 AM
E
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
I rarely use PVC/RNC, and dare I say don't often use bushings on it either, because often the only times I use it, it will have Bell End, and a steel conduit on the other. But yep, required.

352.46 Bushings.
Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.


Mark Heller
"Well - I oughta....." -Jackie Gleason

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,531 Are you busy
190,768 Re: Forum
180,490 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.021s Queries: 14 (0.003s) Memory: 0.9936 MB (Peak: 1.1536 MB) Zlib enabled. Server Time: 2019-04-22 16:46:43 UTC