signal reference grid (high-frequency grid) question ! #44478 11/05/04 03:33 AM
Joined: Oct 2004
Posts: 72
B
bucketman Offline OP
Member
Where in the code book can I find reference to a "high-frequency reference grid system" (or signal-reference grid)? I need to know what kind of grounding point I need to provide in order to prevent unwanted noise.

Thanks!

Work Gear for Electricians and the Trades
Re: signal reference grid (high-frequency grid) question ! #44479 11/05/04 08:15 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
There is nothing in the NEC regarding this design. Check the IEEE colored book series.


Ron
Re: signal reference grid (high-frequency grid) question ! #44480 11/05/04 11:06 AM
Joined: Oct 2003
Posts: 156
D
dereckbc Offline
Member
This is a design issue, and not NEC related. There are many good sources for a SRG. Best guidline is in MIL-HNBK-495A and FIPS-94. There are also some guidelines in IEEE Emerald Book, ITU-T K.27, and ANSI T1.333-2001.

Re: signal reference grid (high-frequency grid) question ! #44481 11/05/04 11:27 AM
Joined: Oct 2003
Posts: 156
D
dereckbc Offline
Member
Bucketman, FWIW, a SRG isn’t bonded to any particular point per se. They can be constructed of either the raised floor grid structure, #6 AWG copper conductor grid under the raised floor, a wire mesh embedded into the concrete or suspended from the ceiling, or a cable rack grid either under a raised floor or suspended from the ceiling. Lots of variables to work with. The important thing is the size of the grid. It depends on the frequency cut-off of interest. The grid is designed on 1/16 of the wavelength, so for a 30 Mhz grid you are looking at something with 2-feet on center. The higher the frequency the smaller the dimensions

As far as bonding or connecting, it is connected to everything like conduits, water pipes, every AC panel EGC bus in the area, all equipment frames, every XO in transformers, every building steel column it passes by, every ground electrode available, etc. The point is not necessarily low impedance to earth, but rather low impedance between any two points on the system and to the power source.

Edited to correct spelling


[This message has been edited by dereckbc (edited 11-05-2004).]

Re: signal reference grid (high-frequency grid) question ! #44482 11/06/04 08:28 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
A general but obsolete/withdrawn NIST document that introduced a lot of terms and concepts for “signal” versus “power” grounding is www.itl.nist.gov/fipspubs/fip94.pdf Early on, authors Lewis and Kalbach were thought to have landed from Mars with some very revolutionary but much-needed discussion on “convergence” of the two widely conflicting systems, and—equally important—the modes of thinking that fostered the original confusion.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,206 Are you busy
206,091 Re: Forum
194,097 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3