A built in microwave if draws more than 50% of the circuit breakers rating then that circuit should not have other loads on it.

If this statment is true would you please find a code reference that would back-up my statement.

I know this rule applies to window A/C units but can not find a NEC section that applies to kitchen appliances such as a built-in microwave.

Thanks a bunch
Edward


Thanks
Edward
Horizontal Ad
Joined: Dec 2002
Posts: 59
S
Member
210.3(2)

Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Thank you for the reply.


Edward


Thanks
Edward
Joined: May 2004
Posts: 162
C
Member
Is the micro a built in if not it is not fastened in place. I think 210.23 (A) (1) may be applicable

(1) Cord-and-Plug-Connected Equipment. The rating of any one cord-and-plug-connected utilization equipment shall not exceed 80 percent of the branch-circuit ampere rating.
Manufactures generally do not install 15 A cord connectors for utilization equipment which operates in excess of 12 A., 16 A for a 20A cord connector etc.(80%)


(2) Utilization Equipment Fastened in Place, addresses specifically that equipment which is fastened in place, such as built in units. It's intent as I read it is to limit that equipments load to not more than 50% of the branch circuit capacity if other cord connected equipment may use the same branch circuit. Most BI Micros will require a individual Branch circuit and the receptacle that is installed in such cases should be a single contact device.

Hope that helps

Charlie


[This message has been edited by cpal (edited 10-01-2004).]


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,295
Joined: December 2000
Top Posters(30 Days)
Popular Topics(Views)
340,808 Are you busy
266,179 Re: Forum
247,119 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5