#42597 09/23/04 04:39 PM
Joined: Mar 2002
Posts: 125
S
Member
I am doing my first I.G system. From what I have read is, you bond all of your grounding conductors together at the transformer. The system is a 480 panel feeding a 120\208 trans. So I should bond them together and seperate the ground and the neutral at the 120 panel. Any help Thanks

Horizontal Ad
#42598 09/23/04 06:55 PM
Joined: Oct 2000
Posts: 2,725
Likes: 1
Broom Pusher and
Member
Sparks30;

Sounds like you have a Step-Down Transformer within the premisis, which will be driving the 208Y/120 VAC Equipment (a Separately Derived System, in other words), you will connect all the Grounding and Grounded Conductors + the Grounding Electrode Conductor and Main Bonding Jumper to the XO Terminal of the Secondary.
At the first Panelboard (actual name for "Sub Panel"), the Grounded Conductor - AKA "Neutral" will terminate on a Bus, which is Isolated / Insulated from the Panelboard's Enclosure (the "Can").

The EGC (Equipment Grounding Conductor) lands on either a Lug, or a Grounding Bus which is Electrically connected to the metallic enclosure - thereby Bonding the Enclosure.

For the IGC (Isolated Grounding Conductor), setup an additional Isolated / Insulated Bus kit - similar to the one for the System's Grounded Conductor (no Electrical connection at the Panelboard), and land the IGCs for both the Branch Circuits and the IGC "Feeder" from the Transformer, on this Bus.

Since there will be quite a few terminations to the "XO" point, get a multi Conductor lug (3 or 4 Conductor) to mount on "XO", land the Grounded Conductor(s), the Grounding Electrode Conductor and the Main Bonding Jumper to "XO".
Use an additional multi Conductor lug on the Transformer's Enclosure, then land the Main Bonding Jumper, the EGCs and the IGCs to this lug.

Below is a drawing that may help - just "convert" the system to an SDS, instead of a PoCo supplied system.
This Drawing is IG Details #1 , which is located in the Technical Reference Section .
Many more items may be found in the same area.

Scott35

[Linked Image]


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#42599 09/23/04 08:13 PM
Joined: Mar 2002
Posts: 125
S
Member
This is great info but the drawings do not match my setup. I have a utility co transformer that feeds a 277/480 switchgear. From there it goes to a 277/480 panel. The 277/40 panel feeds the 277/480 step down transformer 120/208. In this x-former should I bond all grounded and grounding conductors together. Thanks

#42600 09/24/04 08:32 PM
Joined: Oct 2000
Posts: 2,725
Likes: 1
Broom Pusher and
Member
Sparks30;

Quote

In this x-former should I bond all grounded and grounding conductors together

Yes!
[Linked Image]

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Top Posters(30 Days)
Popular Topics(Views)
340,650 Are you busy
266,019 Re: Forum
246,944 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5