ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 117 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#40440 07/20/04 07:01 AM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
Cust.,who is also a builder I work for, wants a sub panel in detached garage via the 3 wire he alresdy has; should I drive a ground rod there?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#40441 07/20/04 09:02 AM
Joined: Oct 2001
Posts: 172
W
Member
Yes, but you should only use the three wire method if there is, and will be, no other metallic paths between the two structures. This includes metal water or gas pipe, telephone or other wires. If you have no other metal connection you should drive a rod or two per requirements, and bond to neutral like service equipment.

#40442 07/20/04 03:00 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Great advice from Watthead, the code section that you need to read would be 250.32(B)(2)

Also no matter if you run a separate EGC or not out to a detached building you must connect grounding electrodes to the panel grounding bar.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#40443 07/20/04 04:19 PM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
s'what I thought - many thanks


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5