Conductors in Parallel #39739 06/28/04 09:31 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline OP
Member
I have seen 800 amp services using two 500 kcmil conductors for each phase. I'm assuming that the ampacity is figured as 430 amps(THHN) X 2 = 860 amps, rather than as being equivalent to one 1000 kcmil conductor at 615 amps. Would three 250 kcmil parallel conductors be 290 amps X 3 = 870 amps?

Dave

Work Gear for Electricians and the Trades
Re: Conductors in Parallel #39740 06/28/04 09:53 PM
Joined: Aug 2001
Posts: 599
N
Nick Offline
Member
The ampacity is figured using the 75 deg table (380A). Times two conductors is 760A. Then article 240.4 is applied allowing the next higher standard fuse size or 800A.

Re: Conductors in Parallel #39741 06/29/04 08:33 AM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
The 75 degree section is used because of the rating of the termination lugs. See 110.14(C).

Remember also to apply 310.15(B)(2)(a) and derate the conductors if you pull all of the paralled conductors in one conduit.

Earl


Earl
Re: Conductors in Parallel #39742 06/29/04 11:04 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
The 75C column must be used because UL does not list Overcurrent Protective Devices for use with conductors based on 90C ampacities.

Re: Conductors in Parallel #39743 06/29/04 04:24 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
One little detail to watch out for is to be sure that the noncontinuous load plus 125% of the continuous load does not exceed 760 amps for parallel 500kcmil. This is usually not the case since most of us don't cut these things real close to the bone & leave some room for future growth.

Tom


Few things are harder to put up with than the annoyance of a good example.

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,009 Are you busy
205,897 Re: Forum
193,951 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3