0 members (), 119 guests, and 14 robots.
#39120 06/09/04 10:25 PM
i need help finding a way to connect 3/0 cu conductors into a siemens 3pole bolt on 100A. molded case circuit breaker.
any ideas would be helpfull thanks
#39121 06/09/04 10:40 PM
Use pin terminals as you said or just splice on some 1, 2, or 3 AWG.
Bob
#39122 06/10/04 08:31 AM
Isn't it odd that code will allow us to splice, butt crimp, or pin terminal conductors oversized for voltage drop , but it is a cardinal sin to clip a couple of strands out of the conductor! UL has approved devices for splices, crimps and pin terminal, but a field adaption is forbidden. If someone (or some organization) would pay the $$$ necessary to get UL or FM to test these terminations, maybe we could all save a few bucks for the rest of our lives. I guess the biggest problem would be how many strands are allowed to be clipped?
Earl
