#38618 05/27/04 10:28 PM
Joined: Feb 2004
Posts: 17
S
Member
when a breaker is listed as 2,3pole on a 277, 480 panel, this means it can be used as overcurrent protection of a 3phase 3wire 480 load or a 1 phase 2 wire 277 load (never done this, but make sence to me.

If you only use to hole of a three wire breaker does it matter which two hole you use? I thinking about the balancing of all three phases in the panel. -thanks

#38619 05/27/04 10:37 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Doesn't matter in your scenario. 240.85 comes into play on non-solidy grounded systems though, such as high-impedance grounded, corner grounded, mid point phase grounded and ungrounded.


Ryan Jackson,
Salt Lake City

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Top Posters(30 Days)
dsk 6
Popular Topics(Views)
284,728 Are you busy
217,352 Re: Forum
203,702 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5