ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 1,501 guests, and 18 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#38618 05/27/04 10:28 PM
Joined: Feb 2004
Posts: 17
S
Member
when a breaker is listed as 2,3pole on a 277, 480 panel, this means it can be used as overcurrent protection of a 3phase 3wire 480 load or a 1 phase 2 wire 277 load (never done this, but make sence to me.

If you only use to hole of a three wire breaker does it matter which two hole you use? I thinking about the balancing of all three phases in the panel. -thanks

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#38619 05/27/04 10:37 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Doesn't matter in your scenario. 240.85 comes into play on non-solidy grounded systems though, such as high-impedance grounded, corner grounded, mid point phase grounded and ungrounded.


Ryan Jackson,
Salt Lake City

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5