compressor terninals #37981 05/12/04 11:50 AM
Joined: May 2001
Posts: 376
F
frank Offline OP
Member
Looking for ideas?I have a 2 ton a/c condenssor where the compressor terminals have heated up and melted.They have become ark damaged to the point that they will not accept a connector. I have cleaned and replaced the terminal conectors on the wire twice now and would rather find a lasting repair than replace the whole unit as I would like to get a few more years from it.So far I'm thinking about using tiny split bolts.
Before i get flamed here I guess i need to state that I am qualified i as a refrigeration mechanic and an industrial electrician. Have been to the trade shows/whole salers ect and the genaric answer is of course to replace the comp/unit for the fear of call backs.
Thanks

Work Gear for Electricians and the Trades
Re: compressor terninals #37982 05/12/04 04:36 PM
Joined: Nov 2003
Posts: 269
E
electricman2 Offline
Member
I assume these are the ΒΌ inch quick connect terminals. Most I have seen are too close together for split bolts, even the smallest ones. I have soldered short pigtails to the terminals and then used wire nuts to connect to the circuit wiring. Not exactly the desired way but cheaper than a new compressor. Good luck


John
Re: compressor terninals #37983 05/12/04 10:37 PM
Joined: Jul 2003
Posts: 394
B
Big Jim Offline
Member
Frank: if you try the soldered pigtails, remember to use soft solder and an iron, if possible. You don't want to cook the lug seals any more than necessary. For you guys that are wondering what brought out that comment, most air conditioning tube fittings are made with hard solder - almost a brazeing rod - and a torch.

Re: compressor terninals #37984 05/13/04 12:20 AM
Joined: Jul 2002
Posts: 8,346
Trumpy Offline
Member
Frank,
Personally, I'd get some new terminal lugs welded on with a spot-welder, using this method the actual weld only takes a second and will withstand a lot higher temperature than a soldered or brazed weld.
Spot-welding is used in the factory, when the compressors are assembled. [Linked Image]

Re: compressor terninals #37985 05/13/04 06:18 AM
Joined: Jan 2004
Posts: 105
C
chi spark Offline
Member
are the posts still intact? Do the terminals consist of a spade with a post attached? I've seen the spade fried, with the round post still sticking out enough. There are solderless terminals for these round posts-I'll try to find and post-I've seen them on hard-starts, and supco kits. No luck yet, I have used the tiny brundy splices before with no guarantee-one has performed for eight years now. Not a lot of clearance in that little compartment.

Hey Trumpy, I'm not much of a welder, but if this is a hermetic, there's only about 3/8" to 5/8" between terminals, I don't know how you could attach the grounding electrode to the terminal without sending current through one or other windings. Have you had luck with that before? It would be a good answer if it didn't compromise motor and fusite integrity.

[This message has been edited by chi spark (edited 05-13-2004).]

Re: compressor terninals #37986 05/13/04 06:23 AM
Joined: Dec 2001
Posts: 300
M
maintenanceguy Offline
Member
Your local hvac supplier will have a kit just for this. It's a set of wires with odd looking screw tight connectors made to grab onto the little bit of terminal that's left.

The counter guy will know exactly what you're looking for.

Re: compressor terninals #37987 05/13/04 06:33 AM
Joined: Apr 2002
Posts: 914
E
Electric Eagle Offline
Member
Like Maintainanceguy said, they make a terminal repair kit just for this application. I have one on my unit. Keep in mind this is just a quick fix, the root cause is that your compressor is worn out. You are pulling more power than it was designed to. I'm just waiting for an HVAC buddy to change out my unit when he has time.

Re: compressor terninals #37988 05/13/04 10:54 PM
Joined: Jul 2002
Posts: 8,346
Trumpy Offline
Member
Chi spark,
A spot-welder looks like this:
[Linked Image]

Re: compressor terninals #37989 05/14/04 09:48 AM
Joined: May 2001
Posts: 376
F
frank Offline OP
Member
Well I'm going to the wholesaler to see about the terminal kit.As already said i asked around and never heard of such animal.As for soldering and welding I'm not sure i can get a good joint with out butchering the refrigerant seals on the hermetic compressor terminals.There is only a 3x4 inch work space in the box so thats plan B if the terminal kit turns out to be no joy. thanks again.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,873 Are you busy
205,730 Re: Forum
193,832 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3