Service Relocation #37690 05/04/04 10:46 PM
Joined: Dec 2003
Posts: 524
Attic Rat Offline OP
Member
... I'm starting a good job,where the H.O. wants me to move the service to the other side of the house..(had to ask the PoCo inspector,..but he said it's OK)as well as upgrade to 200amps..AND wire the newly installed central A/C system..At first,I was gonna bus all the existing home-runs to the new panel location,...then I had an "Epiphany"...or a moment of "clarity"..Why can't I just install a main-lug panel,run 100 amp.SER, and use it as a sub-panel..Sounds easier,and cheaper than running all the home-runs over to the new panel...Does this make sense..??
Russ


.."if it ain't fixed,don't break it...call a Licensed Electrician"
Work Gear for Electricians and the Trades
Re: Service Relocation #37691 05/05/04 12:46 AM
Joined: Feb 2004
Posts: 1,434
Lostazhell Offline
Member
Done all the time out here Russ..... Typically a "blank" will be out in the old meter socket.. Backfeed the bus with a breaker of proper rating for the panel & the feeders you will use & reconnect to a breaker at the new service..

-Randy

Re: Service Relocation #37692 05/05/04 04:26 PM
Joined: Mar 2004
Posts: 76
M
Megawatt Offline
Member
With that distance, it's the best option.
Good Idea !

Re: Service Relocation #37693 05/05/04 06:13 PM
Joined: Mar 2004
Posts: 11
K
kody wilson Offline
Member
you will still need a main breaker in the sub panel enless the main panel is in sight of it.

Re: Service Relocation #37694 05/05/04 06:31 PM
Joined: Dec 2003
Posts: 886
H
hbiss Offline
Member
you will still need a main breaker in the sub panel enless the main panel is in sight of it.

You do? Where does it say that?

-Hal

Re: Service Relocation #37695 05/05/04 06:40 PM
Joined: Jan 2002
Posts: 1,457
E
Electricmanscott Offline
Member
Sounds like a good idea provided existing panel is worth saving. You probably already know that you won't need a main breaker in the sub panel. What table will you use to size the feeder?

Re: Service Relocation #37696 05/05/04 09:46 PM
Joined: Mar 2004
Posts: 11
K
kody wilson Offline
Member
Article 230 chapter seven {230.91}

"The service overcurrent device shall be an integral part of the service disconnecting means or shall be located immediately adjacent thereto."
But we are talking about {feeders} to the sub panel.
I'm just thinking the sub. still needs a disconect right? because the main isn't with in sight and 50'.

Re: Service Relocation #37697 05/05/04 09:49 PM
Joined: Mar 2004
Posts: 11
K
kody wilson Offline
Member
use table 310.15 {b}{6} for sizeing.

Re: Service Relocation #37698 05/09/04 09:17 PM
Joined: Apr 2002
Posts: 189
T
triple Offline
Member
Kody, look up the code definition of a "service" and you will see why the article you referenced does not apply to the subpanel in the case discussed.

…and I’m not even going to get into 310.15(B)(6). If the code making panel is going to do such a half-azzed job of explaining its position, then we as electricians should not be expected to read their collective mind.

Re: Service Relocation #37699 05/09/04 09:55 PM
Joined: Jun 2003
Posts: 681
P
PCBelarge Offline
Member
I agree with Triple, and as for 310.15(B)(6), that is not for the panels past the service equipment. Size the conductors from 310.16 (table).
The definition of service is in Art 100.

Pierre


Pierre Belarge
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
BEAMEUP
BEAMEUP
WA
Posts: 27
Joined: December 2004
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,897 Are you busy
205,757 Re: Forum
193,867 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3