fast start device #3463
08/18/01 11:08 AM
08/18/01 11:08 AM
S
strainsa  Offline OP
Junior Member
Joined: Aug 2001
Posts: 3
When my lights started to momentarily flicker when my new A/C would come on, I called the installer about it. He said they could come out and install a "fast start" or "quick start" device to stop the flicker. Has anyone ever heard of this? If so, will it have any long term harm to my A/C or electical system? I guess I might be at the limit of my electrical service and was wondering how I could really figure that out.

Work Gear for Electricians and the Trades
Re: fast start device #3464
08/18/01 12:28 PM
08/18/01 12:28 PM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
A "quick start" device is really nothing more than a capacitor. What does it do( and more appopriately - How do it know? ) it smooths out the distortion in the phase angle variance when a single phase motor starts up. You see lights flicker because their perfect little 60 cps world has just been altered. Long term harm, Yep, but you won't live that long.

Re: fast start device #3465
08/18/01 08:41 PM
08/18/01 08:41 PM
F
frank  Offline
Member
Joined: May 2001
Posts: 376
windsor ontario canada
i have been in the electrical and refrigeration industry for 10 yrs now and have never herd of a "quick start" i have herd of and used many "hard start" devices however i have never seem them used in this way.they are wired across the compressor capacitor terminals to raise capacitance on compressors that trip the O/Ls during start up.also i have read you can raise capacitance up to but no more than 10% without any long term damage to motor windings.post back and let me know how this works in reducing the flicker effect which by the way is a very common problem.

Re: fast start device #3466
08/18/01 09:31 PM
08/18/01 09:31 PM
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,901
NY, USA
My two cents:

I think we're all on the same page here, but I thought they were called "Soft Start" devices [Linked Image] (Maybe just a local marketing term)

Bill

Re: fast start device #3467
08/18/01 09:42 PM
08/18/01 09:42 PM
G
George Corron  Offline
Member
Joined: May 2001
Posts: 717
Lorton, Va USA
OK, nothing stops the "flicker" effect of a single phase compressor coming on, the Hard start, quick start, soft start whatever you wanna call it kits are meant to reduce phase angle corruption at the unit, for the unit. period = HOWEVER, some manufacturers contend that by making the adjustment at the source of the problem, you reduce the problem away from the source. It will not injure your wiring system, it will only have effect on appliances or devices which are being utilized at that moment, like I said, he ain't gonna live long enough to notice any failures from this minor distortion.

Re: fast start device #3468
08/19/01 04:56 AM
08/19/01 04:56 AM
electure  Offline

Member
Joined: Dec 2000
Posts: 4,274
Fullerton, CA USA
Just make sure that you aren't buying a bill of bull!!

Capacitors are cheap. Don't go buying a new condenser that's "Y2K compliant, quick start, energy saving, as seen on TV...etc." without really assesssing your needs
I once knew a refrig. contractor that would sell an installation kit for a capacitor for $42. The kit consisted of 2 orange wirenuts and a 6-32 screw. (worth at net about 20 cents)

Re: fast start device #3469
08/19/01 09:10 PM
08/19/01 09:10 PM
S
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,360
man, seasoned tradesmen chewin' the 'terminology' rag. [Linked Image]
someone could write a book with all the lingo that comes thru this forum...


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 13
sparky 11
Trumpy 11
Popular Topics(Views)
249,261 Are you busy
187,190 Re: Forum
176,544 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.020s Queries: 14 (0.005s) Memory: 0.9849 MB (Peak: 1.1353 MB) Zlib enabled. Server Time: 2018-09-18 16:05:25 UTC