Emergency / Exit fixtures #34320 02/08/04 03:53 PM
Joined: Feb 2004
Posts: 2
G
gzgerson Offline OP
Junior Member
Hello

I'm new here and have a question on "Emergency / Exit fixtures". Our one story cement block building in Philadelphia Pa has exit signs in each office/room (no windows in offices or meeting rooms). The Exit fixtures are all on one breaker (great for annual battery testing).

After a recent power outage we decided to add emergency lighting in each room. Two ECs
have suggested we replace the "Exit fixtures" with "Exit / Emergency combo fixtures".

One EC said just replace the "Exit fixtures" with "Exit / Emergency combo fixtures", the other EC said they should be wired to the lighting circuit of each room (in case the breaker for that room trips). They both said their proposal was code compliant.

Which one is code compliant?

Thanks for the help:
George


[This message has been edited by gzgerson (edited 02-08-2004).]

[This message has been edited by gzgerson (edited 02-08-2004).]

Work Gear for Electricians and the Trades
Re: Emergency / Exit fixtures #34321 02/08/04 04:16 PM
Joined: Jan 2003
Posts: 1,429
L
LK Offline
Member
George,
Good question, You should put them on the lighting circuit for the area served, ahead of any switches, However there is an exception and I do not have the code book here, so I can't comment, there are others on line, that I am sure will be able to help.

Re: Emergency / Exit fixtures #34322 02/08/04 04:18 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
There are many ways to gain compliance, but the most common way is to install the E-circuits with the general purpose lighting. A dedicated circuit is permitted, but it must be on a generator or other type of uninteruptalbe supply. Refer to 701.11, and you will see that the same circuit is probably the cheapest/easiest way.


Ryan Jackson,
Salt Lake City
Re: Emergency / Exit fixtures #34323 02/08/04 05:25 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
They are both right, kind of, in an open area with 3 or more lighting circuits the emergency battery units may be on a dedicated circuit.

Otherwise the EBUs must be on the lighting circuit feeding the area the EBUs are located in.

Part of 700.12(E) and it's exception.
Quote
700.12(E)........The branch circuit feeding the unit equipment shall be the same branch circuit as that serving the normal lighting in the area and connected ahead of any local switches. The branch circuit that feeds unit equipment shall be clearly identified at the distribution panel. Emergency luminaires (illumination fixtures) that obtain power from a unit equipment and are not part of the unit equipment shall be wired to the unit equipment as required by 700.9 and by one of the wiring methods of Chapter 3.

Exception: In a separate and uninterrupted area supplied by a minimum of three normal lighting circuits, a separate branch circuit for unit equipment shall be permitted if it originates from the same panelboard as that of the normal lighting circuits and is provided with a lock-on feature.

[This message has been edited by iwire (edited 02-08-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Emergency / Exit fixtures #34324 02/08/04 05:40 PM
Joined: Dec 2003
Posts: 59
B
big guy Offline
Member
Exception: In a separate and uninterrupted area supplied by a minimum of three normal lighting circuits, a separate branch circuit for unit equipment shall be permitted if it originates from the same panelboard as that of the normal lighting circuits and is provided with a lock-on feature .

ok what is it a standby systems or a emergency systems
the same thing is in 701.11 (f)

Re: Emergency / Exit fixtures #34325 02/09/04 01:37 AM
Joined: Feb 2004
Posts: 2
G
gzgerson Offline OP
Junior Member
Thanks for all your input. I will check the # of lighting circuits for each area and have the fixtures wired accordingly.

regards:
George


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,034 Are you busy
205,039 Re: Forum
193,154 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3