any exceptions for not having the lens cover for a fixture located over a shower ?is this per (nec) or (ahj) rule ?
|
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
410.4(A) addresses luminiares in wet and damp locations. The location that you describe is a damp one, and therefore the fixture must be listed as such. The only way (that I'm aware of) to obtain this is with a shower lens.
[This message has been edited by Ryan_J (edited 01-22-2004).]
Ryan Jackson, Salt Lake City
|
|
|
|
|
Joined: Jun 2002
Posts: 186
OP
Member
|
Ryan, a saleman came to my office today with a fixture...(progress lighting) he stated the fixture is listed for wet locations (no cover required) I have always installed covers over shower lights.
|
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Thats interesting. I would ask to see the UL information on it before I put one up. Oh, by the way, it would be a good idea to keep some copies of that info on the job and in the truck, because I'm sure your inspector will ask for it.....I would! ![[Linked Image]](https://www.electrical-contractor.net/ubb/biggrin.gif) Let us know what you find, would you?
Ryan Jackson, Salt Lake City
|
|
|
|
|
Joined: Feb 2003
Posts: 169
Member
|
I looked up a few reccessed light fixtures on line, and all the ones I found were approved for damp areas with out a cover. Before I found this I was of the opinion that outdoor reccessed lights had to have closed covers. I've changed my mind. I think the shower could be a wet location if the ceiling/light fixture is low enough to have water splash into it. Then according to 410.4 it would require a closed trim
|
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
I would look at the configuration of the shower. Many of the smaller shower stalls will have splashing water directed into any fixture inside the stall. I would require a watertight fixture cover for these conditions of use. If, however, there is no way for water to be directed into the fixture, then a fixture approved for damp locations would be approved.
Earl
|
|
|
|
|
Joined: Jan 2004
Posts: 91
Member
|
c'mon guys any shower should have a lense that is water tight. all it would take is one fool tossing water in the air to create an electrifiing experience.
|
|
|