Panel Accessibility question... #32405 12/22/03 06:48 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline OP
Member
Have a customer living in a garden apt. complex. With the permission of apt. management, 3 new 20A circuits for recepts (computer, window A/C, and microwave) were installed.

Since each dwelling unit in this complex has an old 4-hole edison base fusebox and a 60 A feeder from a central utility room, the new lines were taken straight to the utility room, where 3 new breakers were installed in the enclosure that housed the 60A 2-pole feeder breaker that feeds (ONLY) this apartment. Installation passed inspection by local AHJ with flying colors several years ago.

Since the installation was done, apartment management has decided to lock the meter room, rendering the service disconnects for electric, water, and gas to each apartment inaccessible. This includes my 3 new branch circuit breakers, as well as many others that other sparkies have added for other tenants over the years.

Is this lack of access to the service disconnect and branch OCPDs now a NEC violation? 230.72(C) seems to indicate so, unless this falls under the exception, which is vaguely worded. Several tenants are complaining about needing to call maintenance and wait forever for someone to unlock a door in order to reset a tripped breaker or shut off the water when a pipe breaks! [Linked Image]

Work Gear for Electricians and the Trades
Re: Panel Accessibility question... #32406 12/22/03 11:26 PM
Joined: Mar 2001
Posts: 333
S
stamcon Offline
Member
I think if the tennants have 24 hour access to the management company, it is legal under the exemption of 230-72(c)(99NEC).


Steve
Re: Panel Accessibility question... #32407 12/22/03 11:46 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline OP
Member
My question about the exception note is that it refers to "the service disconnecting means supplying more than one occupancy". I interpreted this to mean the MAIN service disconnect ahead of all the individual apartment meters/breakers.

Since there are about 30 or so tenant meters/panels in this room, the "6 or less" provision means that these breakers cannot be considered true "service disconnects" for the building. The main disconnect switch feeding the meter bank is in a separate area that has been locked for many years.

[This message has been edited by NJwirenut (edited 12-22-2003).]


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,742 Are you busy
204,967 Re: Forum
193,087 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3