Joined: Feb 2003
Posts: 4
S
ScottM Offline OP
Junior Member
I had a local electric co. install a new 200 amp service today. I needed the new service to get my hot tub up and running. I told the electrician that I already had a 50 amp GFCI breaker installed outside by the tub and that I needed a 50 amp breaker installed at the new service box.Why the hell did he use a 40 amp breaker? I touched it tonight and it is warmer than the others, which are cold. Should I call and have them come back out and replace it or just do it myself?
Scott

Joined: Oct 2000
Posts: 4,081
Likes: 3
Member
Scott,

You should call and ask the Electrician. Anything we could say would be pure speculation.

Bill


Bill

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles
Posts: 349
Joined: April 2004
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,454 Are you busy
231,865 Re: Forum
216,480 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5