im installing a 100 amp sub in poll barn ,im using PVC and pulling wires .. do i need to pull a ground wire with my feeder conductors ,there will be 2 wires and a nuetral in pipe ,i know i have to drive an additional ground rod at the other building

Horizontal Ad
Joined: Aug 2003
Posts: 1,374
R
Moderator
250.32 allows you to use the grounded conductor of the feeder circuit to attach to the grounding electrode of the seperate structure, if you do not pull an equipment grounding conductor.


Ryan Jackson,
Salt Lake City
Joined: May 2002
Posts: 1,716
R
Member
Will there be any other conductive paths to the barn? (ie phone line or metalic water pipe etc...)

If so yes, and you would isolate the neutral from the EGC and the ground rod (GEC)connections.

Even if you are not going to have any other conductive paths right now, it is still the best way to do this. (plan for the future)

Roger

Joined: May 2002
Posts: 1,716
R
Member
I should have also pointed to 250.32 as Ryan did.

Specificaly 250.32(B)

Roger

Joined: Nov 2003
Posts: 7
S
SCS Offline OP
Junior Member
so i should add the EGC
im running 1/0 copper what size should the EGC be ??

Joined: Nov 2003
Posts: 7
S
SCS Offline OP
Junior Member
did i say thank you for the fast reply ??

Joined: Aug 2003
Posts: 1,374
R
Moderator
Your welcome.

If you decide to use an equipment ground, you cannot use the nuetral for attachment to the grounding electrode.

If you do not pull an equipment ground you may use the nuetral for attachment to the grounding elctrode.

Dealer's choice!


Ryan Jackson,
Salt Lake City
Horizontal Ad
Joined: Aug 2003
Posts: 1,374
R
Moderator
I'm sorry i missed half of your question. REmember that EGC's are driven by the size of the breaker, not the size of the conductor. 250.122 tells me that #8 is fine.


Ryan Jackson,
Salt Lake City
Joined: Nov 2003
Posts: 7
S
SCS Offline OP
Junior Member
thanks guys

Joined: May 2002
Posts: 1,716
R
Member
SCS, Welcome to the forum.

I personaly would install the EGC.

Roger

Page 1 of 2 1 2

Link Copied to Clipboard
Featured:

 Electrical
 Clearance

 *
 Tools
 *

 Books

 *

 Test Equipment

 

Advertisement:-Right
Member Spotlight
Posts: 362
Joined: April 2003
Top Posters(30 Days)
Trumpy 5
dsk 1
Popular Topics(Views)
552,930 Are you busy
427,515 Re: Forum
397,988 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5