im installing a 100 amp sub in poll barn ,im using PVC and pulling wires .. do i need to pull a ground wire with my feeder conductors ,there will be 2 wires and a nuetral in pipe ,i know i have to drive an additional ground rod at the other building
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
250.32 allows you to use the grounded conductor of the feeder circuit to attach to the grounding electrode of the seperate structure, if you do not pull an equipment grounding conductor.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Will there be any other conductive paths to the barn? (ie phone line or metalic water pipe etc...)
If so yes, and you would isolate the neutral from the EGC and the ground rod (GEC)connections.
Even if you are not going to have any other conductive paths right now, it is still the best way to do this. (plan for the future)
Roger
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
I should have also pointed to 250.32 as Ryan did.
Specificaly 250.32(B)
Roger
|
|
|
|
Joined: Nov 2003
Posts: 7
OP
Junior Member
|
so i should add the EGC im running 1/0 copper what size should the EGC be ??
|
|
|
|
Joined: Nov 2003
Posts: 7
OP
Junior Member
|
did i say thank you for the fast reply ??
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Your welcome.
If you decide to use an equipment ground, you cannot use the nuetral for attachment to the grounding electrode.
If you do not pull an equipment ground you may use the nuetral for attachment to the grounding elctrode.
Dealer's choice!
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I'm sorry i missed half of your question. REmember that EGC's are driven by the size of the breaker, not the size of the conductor. 250.122 tells me that #8 is fine.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Nov 2003
Posts: 7
OP
Junior Member
|
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
SCS, Welcome to the forum.
I personaly would install the EGC.
Roger
|
|
|
Lostazhell