#28269 08/15/03 12:35 PM
Joined: Nov 2000
Posts: 246
R
rmiell Offline OP
Member
If you have a panelboard rated 22k AIC, and you install a breaker rated only 10k AIC, and assuming no series combo ratings, is the complete setup rated 10k or 22k?

Where is this addressed in the NEC?

Thanks

Rick Miell

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#28270 08/15/03 01:31 PM
Joined: Nov 2000
Posts: 2,148
R
Member
If the available current at the line side of the breaker exceeds 10k, you can't install that breaker. See 110.9. I guess you would have to say that the set-up is only good for the 10k after you install the 10k breaker. It doesn't really change the rating of the panel or the other breakers, but prohibits the use of the panel with the 10k breaker on a system where the available fault current exceeds 10k.
Don


Don(resqcapt19)
#28271 08/15/03 05:10 PM
Joined: Aug 2001
Posts: 7,520
P
Member
Don,
Would the NEC allow a breaker rated lower than the prospective fault current if there is a properly rated OCPD upstream?

We commonly use domestic breakers rated 6000A AIC here on supplies capable of delivering a much higher current. The higher AIC rating of the main cartridge fuse is considered adequate protection against a dead short.

#28272 08/16/03 12:05 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Paul,
If it is a listed and tested "series rated" system, a lower rated breaker may be used. This system cannot be calculated based on let through curves or any other type of calculation. It must be tested by a testing lab and listed.
Don


Don(resqcapt19)
#28273 08/16/03 04:44 AM
Joined: Aug 2001
Posts: 7,520
P
Member
Ah, so only if the actual series combination is listed for such use then. Thanks.