0 members (), 87 guests, and 16 robots.
#27784 07/31/03 11:52 PM
If I feed a 100a main lug panel with say a 40a dp breaker, do I have 40a total capacity? Or do I have 40a available on each leg for 120v loads?
#27785 08/01/03 12:40 AM
Russell,
Look at it this way--
40A @ 240V = 9600 VA
and
9600 VA/120V = 80A
So, you've got 40A on each of the legs.
Cliff
#27786 08/01/03 12:45 AM
If you touch each of the two little screw heads on the circuit breaker where the wires go with the test leads of a voltmeter and it says 208 or 240, you have 80 amps of 120 volt power available. That's assuming you have a neutral too. Of course.
(signed) Sorry. I forgot my name.
#27787 08/01/03 06:36 AM
Thank you Cliff and Bob.