#26924 06/26/03 08:25 AM
Joined: Dec 2002
Posts: 59
S
Member
does anybody here have expereance with back feeding transformers? here's the deal...i have a customer with a 240 volt grounded b 3 phase service. he has an x-ray machine that requires 480 volt. i am going to install a 480 t0 240 volt transformer. i know if i back feed it, i will get the needed 480 volts, but i'm not sure on conductor sizing. is it the same as a normal install? is there anything else i should be aware of? Thanks
richard

#26925 06/26/03 01:56 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
'806 — It's duck soup. Get a 480∆-240∆ dry-type transformer...15kVA and up are fairly common.

If you don't mind a 2MB pdf, see page 21 at http://www.federalpacific.com/literature/drytrans/FPTS-RTB-0701.pdf

Suggest getting a transformer with both FCAN and FCBN taps—they work in the opposite direction for a reverse-fed arrangement. For sensitive electronics, electrostatically shielded units are suggested. If heat is an issue…pick an 80°C-rise transformer on page 27.

For reverse-fed operation DO NOT connect the 240V-side X4 terminal to anything.

Overcurrent protection of 480V windings on a ∆-∆ transformer can be by the usual 125% rating on [only] the 240V source. No system grounding is required by NEC for the 480V side.

If you like, contact me off-board for figuring the kVA-rating, breaker/fuse and conductor sizes needed.

#26926 06/26/03 06:05 PM
Joined: Dec 2002
Posts: 59
S
Member
bjarney
thanks. i'm gonna email you right now.
Richard