Take emergency work break. Buy emergency ice cream bar on wood stick. Discard ice cream by any convenient manner to avoid contamination. {Get spare ice cream bars.} Keep receipts for tax returns. ;-)
#26190 06/02/03 09:11 PM
If you cut the top off you can dip the wire in there too, and then buy a cone instead of a pop!
#26191 06/02/03 10:20 PM
While we're on the subject of noalox,I use cu. for most of my services(residential).
Due to the influence of a previous employer.and out of habit,I use noalox on cu. conductors also.
Is this a bad habit,poor practice?
#26192 06/02/03 10:28 PM
Some of these products are listed for use with aluminum only, others listed for copper/aluminum, and still others listed for copper/copper, or combinations of theses. Look at the instructions. There is at least one compound that is not suitable for copper/copper connections.
Don
Don(resqcapt19)
#26193 06/02/03 10:36 PM
Thanks Don.