What are air terminals as they relate to lightning protection? I've never worked with air terminals or even seen them before.
#25184 04/30/03 02:41 PM
Ron Offline
An air terminal is the rod that stands on top of the roof/parapet/equipment/etc.
You might know it as a lightning rod.
See NFPA 780
In a NFPA compliant system you will find many of these at the roof/etc.
[This message has been edited by Ron (edited 04-30-2003).]
Ron
#25185 04/30/03 04:27 PM
Air terminals are the little pokey things that point upwards.
    [Linked Image from 67.115.161.42]
http://www.harger.com/catalog2002/2_2_1.pdf
[This message has been edited by Bjarney (edited 04-30-2003).]
#25186 04/30/03 04:30 PM
F
Thank you Ron.
#25187 05/01/03 02:41 AM
Bjarney,
Thats a pretty "graphic" warning sign you've got there, I can just feel the pain, looking at the sign!. [Linked Image]
[This message has been edited by Trumpy (edited 05-01-2003).]
#25188 05/01/03 11:21 AM
F
Bjarney-
Thank you for graphic and text.
#25189 05/01/03 01:24 PM
There new air terminals available that have a "mushroom" type head to eliminate the impalement hazard. I didn't see them in the catalog that BJ linked to, but I know that that company has them because the first time I saw them was at their booth at a trade show.
Don
Don(resqcapt19)
#25190 05/01/03 03:34 PM
Ron Offline
Don,
How about this one? http://www.harger.com/catalog2002/2_2_5.pdf
This is the one I currently spec.
Ron
#25191 05/01/03 03:54 PM
Ron,
The one I was thinking about was a mushroom shape, but that one will also prevent the problem.
Don
Don(resqcapt19)
#25192 05/01/03 05:55 PM
I thought the reason a lighting rod comes to a point is becaue it seems to "attract" the lightning bolt better?
If this is true (I don't know), wouldn't this make a blunted rod less effective?
If it doesn't matter....why make the tips so sharp?