#2419 07/13/01 06:53 AM
Joined: Mar 2001
Posts: 2,056
R
Member
No disrespect, doc, but multi-wire circuits are a fact of life. Especially by professionals. It is often amateurs who will run unnecesary neutrals. It is certainly safer to run the extra neutrals, but the reality is this requires larger conduits & boxes. The key is to be aware of multi-wire circuits. (That being said, I'll probably get hit again someday!!) As far as the 40A brkr, a screw-up,indeed.

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#2420 07/13/01 11:11 AM
Joined: Feb 2001
Posts: 62
M
Member
Do GFCI receptacles tolerate multi-wire branch circuits? I've heard stories where they trip all the time? Any truth to those stories?

#2421 07/13/01 11:31 AM
Joined: Nov 2000
Posts: 2,148
R
Member
GFCIs have no problems with line side multiwire circuits. The only GFCI that will work with a load side multiwire circuit is a 2 pole 120/240 volt breaker.
Don(resqcapt19)