bhester,
You've got a lot of good answers for your Q's here - many talented persons in this forum!!!
![[Linked Image]](https://www.electrical-contractor.net/ubb/biggrin.gif)
Maybe this little bit 'o information can help with your last question[s]:
1: As far as circuitry on the 3 wire circuit [basically the home run portion, using the 12/3 NM cable], if you can measure 220 - 240 volts between the black and red wires, then you have setup the homerun circuit OK. That's what you want to have so the grounded conductor [AKA Neutral] does not get overloaded.
In a case where you are using "stacked twins" [4-20 amp 1 pole breakers connected to only two bus poles], then you could connect two seperate 3 wire home runs on the frame, making sure there's 240 volts between the black and red on each home run.
[just threw that in for an FYI
![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif)
].
2: Glad to see that you are planning to limit the maximum number of outlets per circuit!!
NEC does not limit the number of General Purpose [convenience] type receptacles per circuit on the typical single family dwelling, but that's no reason to follow the "Bare-Bones Minimum" of the NEC! Limiting the number of Receptacles is good design. This is the same on any type of circuit [AKA 2 wire circuit or 3 wire circuit].
For lighting, design the circuit[s] so they will not be overloaded if all lights were on at the same time, plus the largest lamp was used [if medium based screw shell fixtures, rate fixture at no less than 150 va].
3: Be sure to connect the circuits so they work on 1/2 the 3 wire [multiwire] circuit properly. This means keep the grounded conductors' connections uniform throughout their circuitry.
Maybe another member can explain this better!
![[Linked Image]](https://www.electrical-contractor.net/ubb/eek.gif)
Basically, the multiwire circuit will be the same as any typical 2 wire circuit, just that the common grounded conductor needs to be spliced and tapped more solidly, plus the need to have the ungrounded conductors connected across both lines - in order to avoid overloading the common grounded conductor [common Neutral].
Please excuse the "Outer Space" explainations! Feel free to comment if needed.